[RE-wrenches] magnum question
Jay
jay.peltz at gmail.com
Wed Apr 1 21:27:23 EDT 2020
Hi Dana,
That depends on the unit.
In my case its a large generator with large loads, the inverters being just one of the loads. I can’t load one phase with 8kw, that would overload one phase. Splitting the load to 2 phases, is within the capacity of the generator and within the total loads
I know I can do the inverters the way I want, what I dont know is if you can have 2 x 120v magnum inverters both as master with a single controller.
Jay
> On Apr 1, 2020, at 5:28 PM, Dana Orzel <dana at solarwork.com> wrote:
>
> I have been informed [long ago] that not equally weighting a generators output can cause excessive & uneven wear on the windings of a generator.
> Way Back in the day, folks [old wrenches] used to place an additional load [hot water element, heat lamps...] on the unused leg to balance out a 240 vac gen that was only using one 120v leg for inverter /battery charging on a 240 only generator. Simple but effective though not very fuel thrifty.
>
> I am open to dispelling this anecdote/old wife's tale, if anyone can confirm or dispute this. It makes sense to me overall.
>
>
>
> Dana Orzel Great Solar Works, Inc.
> C - 208.721.7003 dana at solarwork.com
> Idaho Contractor - # 028765 Idaho PV # 028374
> NABCEP # 051112-136 www.solarwork.com
> "Responsible Technologies for Responsible People since 1988"
> Please consider the environment before printing this email.
>
>
> -----Original Message-----
> From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of jay
> Sent: Wednesday, April 1, 2020 5:39 PM
> To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
> Subject: [RE-wrenches] magnum question
>
> Hi All,
>
> My question is can a single Magnum remote run 2 inverters each as master for 120v?
>
>
> I’ve got a client with a 3 phase generator, and I need two phases, but I don’t need 240v.
>
>
> 1. I can’t change the generator
> 2. Two phases because I can’t load one phase that heavily.
>
> I can do 2 Outback FXR’s each as a master, but I’d need to have 2 Mate3S’s.
>
> But I don’t know if magnum has that possiblity?
>
> Thanks
>
> jay
>
> Peltz Power
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
More information about the RE-Wrenches
mailing list