[RE-wrenches] Brown-Out Prone Opportunity Charging
Starlight Solar Power Systems
larry at starlightsolar.com
Mon Mar 16 13:05:45 EDT 2020
Did you mean to say LFP? It depends on who made the battery. LFP batteries can be charged using CC/CV. Some, like the Elite PS/GBS battery packages can accept a simple CV power supply of 3.65 Vpc.
The inverter is always on and isolated from the grid so it’s not affected by poor power quality unless you allow ripple or spikes to the battery system. That should be protected at the AC input of your charger/PS and PS filtering.
What is the daily power consumption? If the battery and PS are sized to meet your loads, then it won’t matter when the grid is available. Grid Outages longer than you design for can be backed up with a generator.
Larry Crutcher
Starlight Solar Power Systems
On Mar 13, 2020, at 6:09 PM, Jeff Clearwater <jeffc at villagepowerdesign.com> wrote:
Thanks All,
Mick and Tump - I'll look into the Victron - good suggestion - Thanks!
Chris - I'm not sure a transformer will buffer the spikes and frequency but just pass them on - others?
Larry and Jerry - If I were to go with the separate battery charger/PS approach - what specific 48 V LFeP battery Charger/PS might you recommend and how to protect it with what sort of surge and LV equipment? If either the inverter or PS/Charger is protected within too narrow a range then it might defeat the purpose - wanting to maximize pulling in as much opportunity charging as we can get.
Seems to me like there might be a market for a highly tolerant battery charger between 160-260 VAC and frequency tolerant as well - something bulletproof we could put on these systems - perhaps that is the Victron - but I'd rather have it in a separate beefy battery charger then risk the inverters - especially if we are going to buffer the customer from the grid with the battery/inverter system.
For instance we have a hospital that can only use the available grid for the office but they can't risk it for their hospital equipment. But If I could pull the grid into batteries safely and always power their loads with the high reliability battery/inverter system - now we are talking.
So specific 48V battery chargers that can take it? Any equipment out there anyone is aware of?
Thanks!
Jeff
Tump wrote on 3/13/20 2:47 PM:
> Check out the Victron line of Chargers as well as the inverter charger units. AC in 187-265 45-65 Hz. for the inverters 230V/50Hz, inverter.
> Please feel free to e mail me 4 additional info. Great BT support / internet access. well thought out product.
>> On Mar 13, 2020, at 5:11 PM, Jerry Shafer <jerrysgarage01 at gmail.com <mailto:jerrysgarage01 at gmail.com>> wrote:
>>
>> Jeff
>> I have been there too in most cases we have programmed in the VAC max/mins with tighter setting so as the grid starts to go we just disconnect. I did just do a charger instead of the inverter because the grid was generally low on frequency but the charger just charged and l see it on optics when that happens
>> Jerry
>>
>> On Fri, Mar 13, 2020, 12:03 PM Jeff Clearwater <jeffc at villagepowerdesign.com <mailto:jeffc at villagepowerdesign.com>> wrote:
>> Good Day Esteemed Wrenchers,
>>
>> So we are doing more work in developing countries where the grid is super unreliable but on for some hours almost daily.
>>
>> So let's say we have a grid that's on 9 AM - 11 AM and 4 PM - 7 PM each day but often browns-out during those hours and comes on and off during those hours. 230 VAC voltage can drop to 160-180 periodically or go above 260 in spikes.
>>
>> The present practice in many of these situations is for battery based system designers/installers is to set up an off-grid system in parallel to the mains but not relying on them - so the grid AC IN is not connected. They just install a transfer switch and manually switch or they wire a critical loads panel to the solar.
>>
>> This avoids constant switching and nuisance shut-downs from the battery inverter and protects it from burning out trying to handle the grid.
>>
>> MY QUESTION:
>>
>> I'm wondering what we can do to use the grid when it is up for opportunity charging of the batteries while at the same time not subjecting our nice new battery inverters to constant brown-out tripping and possibly long term damage.
>>
>> So question #1 - Is anyone using existing battery inverters but succesfully navigating such a grid variablity settings such that you are able to take advantage of the grid even if browning out often?
>>
>> or question #2 - Can we add some sort of high Voltage and Frequency tolerant battery charger to the system - keep the battery inverter/charger off grid - but charge the batteries from something able to handle the wonky grid without constantly nuisance charging or burning itself up?
>>
>> Your thoughts and wisdom I await!!!
>>
>> Best,
>>
>> Jeff
>>
>>
>> --
>> ~~~~~~~~~~~
>> Jeff Clearwater
>> Village Power Design
>> linkedin <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
>> www.villagepowerdesign.com <http://www.villagepowerdesign.com/>
>> cell - 413-559-9763
>> ~~~~~~~~~~~~~~~~~~~~~~~
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200316/73b7f17d/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: smime.p7s
Type: application/pkcs7-signature
Size: 1380 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200316/73b7f17d/attachment.p7s>
More information about the RE-Wrenches
mailing list