[RE-wrenches] Brown-Out Prone Opportunity Charging

Jeff Clearwater jeffc at villagepowerdesign.com
Fri Mar 13 21:13:55 EDT 2020


Ahh I see now the Victron does have a line of Chargers that are not also 
Inverters. Thanks!

Anyone else with experience with specific equipment?

Thanks again,

Jeff


Jeff Clearwater wrote on 3/13/20 6:09 PM:

> Thanks All,
>
> Mick and Tump - I'll look into the Victron - good suggestion - Thanks!
>
> Chris - I'm not sure a transformer will buffer the spikes and 
> frequency but just pass them on - others?
>
> Larry and Jerry - If I were to go with the separate battery charger/PS 
> approach - what specific  48 V  LFeP battery Charger/PS might you 
> recommend and how to protect it with what sort of surge and LV 
> equipment?  If either the inverter or PS/Charger is protected within 
> too narrow a range then it might defeat the purpose - wanting to 
> maximize pulling in as much opportunity charging as we can get.
>
> Seems to me like there might be a market for a highly tolerant battery 
> charger between 160-260 VAC and frequency tolerant as well - something 
> bulletproof we could put on these systems - perhaps that is the 
> Victron - but I'd rather have it in a separate beefy battery charger 
> then risk the inverters - especially if we are going to buffer the 
> customer from the grid with the battery/inverter system.
>
> For instance we have a hospital that can only use the available grid 
> for the office but they can't risk it for their hospital equipment.  
> But If I could pull the grid into batteries safely and always power 
> their loads with the high reliability battery/inverter system - now we 
> are talking.
>
> So specific 48V battery chargers that can take it? Any equipment out 
> there anyone is aware of?
>
> Thanks!
>
> Jeff
>
> Tump wrote on 3/13/20 2:47 PM:
>> Check out the Victron line of Chargers as well as the inverter 
>> charger units. AC in 187-265 45-65 Hz. for the inverters 230V/50Hz, 
>> inverter.
>> Please feel free to e mail me 4 additional info. Great BT support / 
>> internet access. well thought out product.
>>> On Mar 13, 2020, at 5:11 PM, Jerry Shafer <jerrysgarage01 at gmail.com 
>>> <mailto:jerrysgarage01 at gmail.com>> wrote:
>>>
>>> Jeff
>>> I have been there too in most cases we have programmed in the VAC 
>>> max/mins with tighter setting so as the grid starts to go we just 
>>> disconnect. I did just do a charger instead of the inverter because 
>>> the grid was generally low on frequency but the charger just charged 
>>> and l see it on optics when that happens
>>> Jerry
>>>
>>> On Fri, Mar 13, 2020, 12:03 PM Jeff Clearwater 
>>> <jeffc at villagepowerdesign.com <mailto:jeffc at villagepowerdesign.com>> 
>>> wrote:
>>>
>>>     Good Day Esteemed Wrenchers,
>>>
>>>     So we are doing more work in developing countries where the grid
>>>     is super unreliable but on for some hours almost daily.
>>>
>>>     So let's say we have a grid that's on 9 AM - 11 AM and 4 PM - 7
>>>     PM each day but often browns-out during those hours and comes on
>>>     and off during those hours. 230 VAC voltage can drop to 160-180
>>>     periodically or go above 260 in spikes.
>>>
>>>     The present practice in many of these situations is for battery
>>>     based system designers/installers is to set up an off-grid
>>>     system in parallel to the mains but not relying on them - so the
>>>     grid AC IN is not connected.  They just install a transfer
>>>     switch and manually switch or they wire a critical loads panel
>>>     to the solar.
>>>
>>>     This avoids constant switching and nuisance shut-downs from the
>>>     battery inverter and protects it from burning out trying to
>>>     handle the grid.
>>>
>>>     MY QUESTION:
>>>
>>>     I'm wondering what we can do to use the grid when it is up for
>>>     opportunity charging of the batteries while at the same time not
>>>     subjecting our nice new battery inverters to constant brown-out
>>>     tripping and possibly long term damage.
>>>
>>>     So question #1 - Is anyone using existing battery inverters but
>>>     succesfully navigating such a grid variablity settings such that
>>>     you are able to take advantage of the grid even if browning out
>>>     often?
>>>
>>>     or question #2 - Can we add some sort of high Voltage and
>>>     Frequency tolerant battery charger to the system - keep the
>>>     battery inverter/charger off grid - but charge the batteries
>>>     from something able to handle the wonky grid without constantly
>>>     nuisance charging or burning itself up?
>>>
>>>     Your thoughts and wisdom I await!!!
>>>
>>>     Best,
>>>
>>>     Jeff
>>>
>>>
>>>     -- 
>>>     ~~~~~~~~~~~
>>>     Jeff Clearwater
>>>     Village Power Design
>>>     linkedin <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
>>>     www.villagepowerdesign.com <http://www.villagepowerdesign.com/>
>>>     cell - 413-559-9763
>>>     ~~~~~~~~~~~~~~~~~~~~~~~
>>>     _______________________________________________
>>>     List sponsored by Redwood Alliance
>>>
>>>     List Address: RE-wrenches at lists.re-wrenches.org
>>>     <mailto:RE-wrenches at lists.re-wrenches.org>
>>>
>>>     Change listserver email address & settings:
>>>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>>     List-Archive:
>>>     http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>>     List rules & etiquette:
>>>     www.re-wrenches.org/etiquette.htm
>>>     <http://www.re-wrenches.org/etiquette.htm>
>>>
>>>     Check out or update participant bios:
>>>     www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org 
>>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive: 
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>
>>> *Tump at swnl.net 
>>> <blocked::mailto:Tump at swnl.net%22%20%5Co%20%22blocked::mailto:Tump at swnl.net>**www.SWNL.net* 
>>> <blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
>>> Solarwinds Northernlights *//*
>>> */       Serving Mid Coast Maine & Northern California/**/
>>> /**/ 207-832-7574   Cl. 610-517-8401 /*
>>> *//**/Blair "TUMP" May/*
>>>
>>> */     ********  MAINE'S CHARTER ********
>>> /**//**/NABCEP    "Certified PV Installer"/**/
>>> /**/
>>>   ********  MAINE'S CHARTER ********
>>> /**/Trace Xantrex "Certified" Dealer / Installer"/*
>>>
>>>
>>
>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address:RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>
> -- 
> ~~~~~~~~~~~
> Jeff Clearwater
> Village Power Design
> linkedin <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
> www.villagepowerdesign.com <http://www.villagepowerdesign.com>
> cell - 413-559-9763
> ~~~~~~~~~~~~~~~~~~~~~~~
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>


-- 
~~~~~~~~~~~
Jeff Clearwater
Village Power Design
linkedin <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
www.villagepowerdesign.com <http://www.villagepowerdesign.com>
cell - 413-559-9763
~~~~~~~~~~~~~~~~~~~~~~~
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200313/2b9132a5/attachment.htm>


More information about the RE-Wrenches mailing list