This points out the problem of inconsistent interpretation due in part
to conflicting or unclear language. I always like to ask how many
basements have protection around the NM conductors running through and
along the rafters. I know several people on CMPs are on this listserv.
I am hoping that they can add some clear language, and not leave it to a
footnote for implementing this aspect of the NEC.
On 2/13/2020 4:42 PM, Ray wrote:
>
> It all comes down to where you install the PV disconnect. We put it
> on the wall before the conductors enter the building or at the array,
> therefore 690 doesn't apply. Proper signage is required indicating
> multiple power sources and listing the locations of their disconnects.
>
> Also, this isn't just my opinion, many others on the list have said
> this, including folks involved in the code writing process, and the
> code says this. The fact that your inspector didn't catch the note on
> the figure is to be expected, as it is not out in flashing neon
> lights. It is however a clear statement of where 690 stops: at the PV
> disconnect.
>
> Unfortunately, this is not further clarified in 2020 from what I can
> tell, so we will all continue to suffer inspectors incorrectly
> expecting 690.12 on ground mounted systems. I would politely ask your
> inspector to review that ruling with his higher ups. We can't start
> setting precedents that are unreasonable and incorrect. The array
> wiring is already required to be protected by either height,
> protective panels or fencing.
>
> Ray Walters
> Remote Solar
> 303 505-8760
> On 2/13/20 1:56 PM, Christopher Warfel wrote:
>>
>> Ray, I spent a bit of time today with a person who inspects for
>> several state renewable energy programs and to summarize, this person
>> said the opposite of what you said, and finish saying "seems pretty
>> clear cut". We did review three sections of 690, and one from 705.
>> I pointed out that these are not controlled conductors as I interpret
>> them but they should have been defined. I did not see any earlier
>> posts regarding this, so I apologize for the redundancy.
>>
>> On 2/13/2020 3:16 PM, Ray wrote:
>>>
>>> This has been discussed to death in previous Wrench strings. Just
>>> to cut to the chase:
>>>
>>> please review NEC 2017, Figure 690.1(b) Note:(2). /The PV system
>>> disconnect in these diagrams separates the PV system from all other
>>> systems.//
>>> /
>>>
>>> The inverter, charge controller, batteries etc are no longer part of
>>> article 690, and are not subject to its requirements. Look at
>>> articles 705, 706, and 480 for guidance for those _/other systems/_.
>>>
>>> /Ray Walters/
>>> Remote Solar
>>> 303 505-8760
>>> On 2/13/20 12:55 PM, Dave Angelini Offgrid Solar wrote:
>>>> Hi Chris,
>>>>
>>>> A few times and my back-up with a schneider system is their rapid
>>>> shutdown. In the end the inspector comes around and realizes there is
>>>> little gain for an offgrid ground mounted array for fireman. You do have to
>>>> educate them and if they are insistent on being a bonehead, install the RS
>>>> for the inspection and then use the box for the next one or sell it.
>>>>
>>>> After almost 30 years offgrid the last thing I want is something that can
>>>> fault out the solar or worse when I am away. Networks can be the enemy at
>>>> times. Less is more offgrid in my opinion.
>>>>
>>>>
>>>> Dave Angelini Offgrid Solar
>>>> "we go where powerlines don't"
>>>> http://members.sti.net/offgridsolar/
>>>> e-mailoffgridsolar at sti.net
>>>> text 209 813 0060
>>>>
>>>> On Thu, 13 Feb 2020 13:07:53 -0500, Christopher Warfel
>>>> <cwarfel at entech-engineering.com> wrote:
>>>>> I got involved in a long discussion on Rapid Shutdown compliance for
>>>>> battery multimode, grid interconnect inverters that have a ground
>>>>> mounted array. At one point, ground mounted array was not supposed to
>>>>> be subject to Rapid Shutdown unless there were dc conductors on the
>>>>> building. NEC 2017 seems to say it is if conductors are 3' in or on
>>>>> buildings. The intent of Rapid Shutdown was supposed to protect fire
>>>>> fighters from exposure to high dc voltage when the array was on a roof.
>>>>> Every code cycle it morphs into something a little different. Has
>>>>> anyone had to confront this situation, and was this type of project
>>>>> subject to Rapid Shutdown? Thanks in advance for any clarity on this.
>>>>> Chris
>>>>>
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>>
>>>>> List Address:RE-wrenches at lists.re-wrenches.org
>>>>>
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>
>>>>> List-Archive:
>>>>>
>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>> List rules & etiquette:
>>>>> www.re-wrenches.org/etiquette.htm
>>>>>
>>>>> Check out or update participant bios:
>>>>> www.members.re-wrenches.org
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> List Address:RE-wrenches at lists.re-wrenches.org
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out or update participant bios:
>>>> www.members.re-wrenches.org
>>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address:RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address:RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200213/7d5c1494/attachment.htm>
More information about the RE-Wrenches
mailing list