[RE-wrenches] Tripping gfi
Jerry Shafer
jerrysgarage01 at gmail.com
Tue Jan 14 22:19:48 EST 2020
Ray
Yes you can have a GFI trip as a result of something on the AC side, I had
a hard line data line cause a trip of a GFI even though you would not see
anything on a meter, had to use a optical bridge to connect, granted this
was Sunpower 327's on a Outback 7200 off grid but it can happen. This is
not to say that there is not a problem with the dryer however, just that
there are other possibilities.
Jerry
On Tue, Jan 14, 2020 at 4:51 PM Ray <ray at solarray.com> wrote:
> If there is any current flow between DC negative and ground anywhere in
> the system, it will trip. I would check the dryer for a ground fault, and
> I would check the system to make sure Neutral is not bonded to ground in
> more than one place (very common). Most importantly, I would make sure that
> negative is not bonded anywhere except at the DC GFI in the controller.
>
> My guess is that DC is bonded at the negative shunt as is normal with many
> DC load centers, and that the dryer is a big enough load that pulls enough
> DC amps, so that some of DC negative is flowing back through the ground.
> Probably doesn't trip normally, because at lower loads, less than an amp is
> flowing on the ground.
>
> Just guessing,
>
> Ray Walters
> Remote Solar
> 303 505-8760
>
> On 1/14/20 7:03 PM, Mac Lewis wrote:
>
> Hi wrenches,
>
> I've got an off grid customer that has an external PV GFI breaker in his
> charge controller that trips when the dryer is on. He snuck in an electric
> dryer uggh
>
> However, I am curious what the mechanism might be to cause the trip. Will
> a ground fault on the AC side of an inverter trip a PV GFI on a charge
> controller?
>
> I haven't dug too deep into this yet but maybe someone else has seen this.
>
>
> Thanks in advance for your help.
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200114/2954f7d5/attachment.htm>
More information about the RE-Wrenches
mailing list