Hi Scot and Mike,
Yes It is terribly worded - an AHJ could easily read it and come away=20
with the impression that only the TL and TriPower required the neutral=20
only for instrumentation and voltage and phase detection - implying the=20
rest used the neutral for current.
And your right what do the x's even mean?
I see the SMA author to be Chris Schwegler authored on July 19th, 2019.=20
Mike, can you send back to him for a re-write as this won't hold it's=20
water to AHJs going forward.
Thanks!
Jeff
scot.arey at solarcentex.com wrote on 11/26/19 6:42 AM:
> Mike,
>
> Thanks for posting the note, but I find the wording to be less than=20
> fully clear. According to this note, the =E2=80=9CThe transformer-less se=
ries=20
> of inverters named Sunny Boy TL-US-12, Sunny Boy TL-US-22 and Sunny=20
> Tripower 12/15/20/24000TL-US-10 have a neutral connection that is=20
> required at installation for instrumentation, voltage and phase=20
> detection only.=E2=80=9D
>
> There is no mention of the -41 inverter also using the neutral for=20
> reference only, even though the note is =E2=80=9Capplicable to the follow=
ing=20
> inverter types=E2=80=9D and that shows the -41
>
> Also, the table has these green x marks but no annotation of what the=20
> green x indicates.
>
> Can you clarify, please?
>
> simple signature block
>
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On=20
> Behalf Of *Harry Mahon
> *Sent:* Thursday, November 14, 2019 11:02 AM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>; Jeff Clearwater=20
> <jeffc at villagepowerdesign.com>
> *Subject:* Re: [RE-wrenches] 705.95(B) and Sunny Boys - current on=20
> Neutral?
>
> Lloyd =E2=80=93 great find!
>
> I am attaching a updated note that specifically calls out current=20
> products but has less code detail.
>
> Best regards =E2=80=93
>
> Mike
>
> SMA America
> Michael Mahon
> Technical Trainer, Solar Academy
> 6020 West Oaks Boulevard, Suite 300
>
> Rocklin, CA 95765
>
> U.S.A.
> Mobile: +1 916 918 9412_
> www.SMA-America.com <http://www.sma-america.com/>_
>
> __
>
> Solar Academy: https://solaracademy.sma.de/en.html
>
> SMA America Solar Academy webinars:
>
> https://solaracademy.sma.de/en/courses.html
>
> Choose "English" and "Online" as filters.
>
> http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/facebook.jpg=
=20
> <http://www.facebook.com/pages/SMA-America/140290312717395>http://sma-pla=
net.sma.de/fileadmin/fm-dam/infos/social_media/twitter.jpg=20
> <http://twitter.com/SMA_America>=20
> http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/wordpress.jp=
g=20
> <http://www.smainverted.com/> Linkedin Logo=20
> <http://www.linkedin.com/company/364675>=20
> http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/youtube.jpg =
> <http://www.youtube.com/playlist?list=3DPL840A5336CAC32332>=20
> SMAAFORUM_ICON <http://smaadvance.com/signup/>
>
> cid:image008.jpg at 01D54D07.DC1BFFF0=20
> <https://eur02.safelinks.protection.outlook.com/?url=3Dhttps%3A%2F%2Fwww.=
sma-america.com%2Fhome-systems%2Fpv-solar-and-storage-solutions.html&data=
=3D02%7C01%7CMichael.Mahon%40sma-america.com%7Cc4bcd59d55584c70681208d71b72=
e485%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C637008052588484449&sdata=
=3DitzAGcXAYe0xd5Zhzjuljm6dijJW%2FRGtItHrvxRkrTI%3D&reserved=3D0>
>
> This email and any attachments thereto may contain SMA America, LLC=20
> confidential, privileged and private material for the sole use of the=20
> intended recipient. Any review, copying, or distribution of this email=20
> (or any attachments thereto) by others is strictly prohibited. If you=20
> are not the intended recipient, please contact the sender immediately=20
> and permanently delete the original and any copies of this email and=20
> any attachments thereto. Thank you.
>
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org=20
> <mailto:re-wrenches-bounces at lists.re-wrenches.org>> *On Behalf Of=20
> *Lloyd Hoffstatter
> *Sent:* Wednesday, November 13, 2019 10:38 AM
> *To:* Jeff Clearwater <jeffc at villagepowerdesign.com=20
> <mailto:jeffc at villagepowerdesign.com>>; RE-wrenches=20
> <re-wrenches at lists.re-wrenches.org=20
> <mailto:re-wrenches at lists.re-wrenches.org>>
> *Subject:* Re: [RE-wrenches] 705.95(B) and Sunny Boys - current on=20
> Neutral?
>
> Jeff,
>
> An oldie but attached tech note explains.
>
> May Need to upsize G / N =C2=A0for voltage drop depending on run=E2=80=A6
>
> Best regards,
>
> Lloyd
>
> Lloyd Hoffstatter
>
> Sunstruck Consulting
>
> Sent from Mail=20
> <https://eur02.safelinks.protection.outlook.com/?url=3Dhttps%3A%2F%2Fgo.m=
icrosoft.com%2Ffwlink%2F%3FLinkId%3D550986&data=3D02%7C01%7Cmichael.mahon%4=
0sma-america.com%7Ca57263d3340c445bd5ce08d76860354c%7Ca059b96c28294d1188374=
cc1ff84735d%7C0%7C0%7C637092634734737930&sdata=3DljnPZYRGhPwgRSsi3yM%2BI46x=
1iUvt52uQ8DtHvidzvw%3D&reserved=3D0>=20
> for Windows 10
>
> ------------------------------------------------------------------------
>
> *From:*RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org=20
> <mailto:re-wrenches-bounces at lists.re-wrenches.org>> on behalf of Jeff=20
> Clearwater <jeffc at villagepowerdesign.com=20
> <mailto:jeffc at villagepowerdesign.com>>
> *Sent:* Wednesday, November 13, 2019 12:00:37 PM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org=20
> <mailto:re-wrenches at lists.re-wrenches.org>>
> *Subject:* [RE-wrenches] 705.95(B) and Sunny Boys - current on Neutral?
>
> Hey Folks,
>
> So does anyone have a reference I can show my AJH as to whether there=20
> is any current on the neutral of a single phase 240 VAC SB 7.7-40=20
> inverter?
>
> 705.95(B) states:
>
> *Neutral Conductor for Instrumentation, Voltage
> Detection or Phase Detection. *A conductor used solely for
> instrumentation, voltage detection, or phase detection and
> connected to a single-phase or 3-phase utility-interactive
> inverter, shall be permitted to be sized at less than the
> ampacity of the other current-carrying conductors and shall
> be sized equal to or larger than the equipment grounding
> conductor.
>
> Be great not have to run 3/0 wire to my dedicated PV subpanel with 5=20
> SB7.7s.=C2=A0 At 200 Amps I could use 6 AWG according to 705.95.=C2=A0 A =
huge=20
> savings in wire pull hassle not to mention copper.
>
> Are there any other practical considerations for those SBs to operate=20
> well if I were to go that low with the neutral?
>
> Anybody have any field experience with AJHs on this?
>
> Thanks,
>
> Jeff
>
> ~~~~~~~~~~~
>
> Jeff Clearwater
> Village Power Design
> linkedin=20
> <https://eur02.safelinks.protection.outlook.com/?url=3Dhttps%3A%2F%2Fwww.=
linkedin.com%2Fin%2Fjeff-clearwater-0622a312%2F&data=3D02%7C01%7Cmichael.ma=
hon%40sma-america.com%7Ca57263d3340c445bd5ce08d76860354c%7Ca059b96c28294d11=
88374cc1ff84735d%7C0%7C0%7C637092634734747920&sdata=3Dp3O8JIapfJi4lWUaxtjir=
6oD0Nfss%2FvzCc%2BmO6DhkIc%3D&reserved=3D0>=20
>
> www.villagepowerdesign.com=20
> <https://eur02.safelinks.protection.outlook.com/?url=3Dhttp%3A%2F%2Fwww.v=
illagepowerdesign.com&data=3D02%7C01%7Cmichael.mahon%40sma-america.com%7Ca5=
7263d3340c445bd5ce08d76860354c%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7=
C637092634734747920&sdata=3DnAk%2FP4sQtocN2rmE64IfGo5BkOo1gemXIBVpP1nWXII%3=
D&reserved=3D0>
> cell - 413-559-9763
> ~~~~~~~~~~~~~~~~~~~~~~~
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.o=
rg/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.=
org/attachments/20191126/21fe9935/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 26768 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.=
org/attachments/20191126/21fe9935/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.jpg
Type: image/jpeg
Size: 855 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.=
org/attachments/20191126/21fe9935/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.jpg
Type: image/jpeg
Size: 846 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.=
org/attachments/20191126/21fe9935/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.jpg
Type: image/jpeg
Size: 809 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.=
org/attachments/20191126/21fe9935/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.jpg
Type: image/jpeg
Size: 856 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.=
org/attachments/20191126/21fe9935/attachment-0003.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.jpg
Type: image/jpeg
Size: 961 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.=
org/attachments/20191126/21fe9935/attachment-0004.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 747 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.=
org/attachments/20191126/21fe9935/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.jpg
Type: image/jpeg
Size: 41392 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.=
org/attachments/20191126/21fe9935/attachment-0005.jpg>
More information about the RE-Wrenches
mailing list