[RE-wrenches] Conext SW Mystery

Steve Higgins steve at surrette.com
Mon Nov 18 23:59:11 EST 2019


Aaron,

Ditto what Ray said... I think it's a LVD, LBCO... but could also be a
connection cabling issue have them put a wrench on the terminals,  have
them loosen first, then retorque, don't just have them "tug test" them as
if they are already welded it'll look like a good connection...   Make sure
they do this with the system off and not charging as a spark here could
ignite hydrogen, this would cause a battery to possibly explode...   Not
pretty or fun!

 If LVD or LBCO is set too high, that would prevent the Gen from Auto
Starting.


<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
Steve Higgins ⋅ Technical Services Manager
t +1.902.597.4020  m +1.206.790.5840
f +1.902.597.8447  e steve at surrette.com
<#SignatureSanitizer_SafeHtmlFilter_> <http://www.facebook.com/RollsBattery>
<http://www.facebook.com/RollsBattery> <http://www.twitter.com/RollsBattery>
<https://www.youtube.com/user/RollsBattery>
<https://www.linkedin.com/company/rolls-battery-engineering>
<http://www.instagram.com/RollsBattery>
<http://www.instagram.com/RollsBattery>
<http://www.instagram.com/RollsBattery>

------------------------------
*Become a Certified PV Professional. Register for* *NABCEP CEC 2020*
<http://rollsbattery.com/nabcep2020> *using promo code* *20RBE*
<http://rollsbattery.com/nabcep2020>
------------------------------
CONFIDENTIALITY: The information transmitted herein is intended only for
the addressee and may contain confidential, proprietary and/or privileged
material. Any unauthorized review, distribution or other use of or the
taking of any action in reliance upon this information is prohibited. If
you receive this email in error, please contact the sender and delete or
destroy this message and all copies.
------------------------------


On Mon, Nov 18, 2019 at 8:52 PM Ray <ray at solarray.com> wrote:

> Totally sounds like Low voltage disconnect to me.  Many, Many times the
> generator does not start when it should or connect to the inverter.  I've
> had 2 systems recently, that both shut down, 1 had the LVD set really high,
> higher than the gen start, so that definitely didn't work.  The next one
> would start the generator when required, but the generator voltage
> regulation was incorrect, so the inverter would never connect to it.
> Thinking the Ecogen is going to save the day is going to be recipe for
> disaster;  over the years I've come to despise the Ecogen.  I'm seeing 50%
> failures, and some of the failures are catastrophic, complete engine
> failures.  I don't have a suggested replacement, other than go big enough
> (+20 kW) to get into the 1800 rpm water cooled equipment, or just get a
> decent portable.  At least with a portable, you can haul it in for service.
>
> Ray Walters
> Remote Solar
> 303 505-8760
>
> On 11/18/19 8:00 PM, Aaron Mandelkorn wrote:
>
> This is a strange one.  I have a Schneider SW 4024 installed in a remote
> area of Colorado.  Cold and high altitude.  Since the fall every time my
> customer has gone out to her cabin she noticed that the inverter is off.
> She proceeded to turn the unit back on by pressing the button on the SW.
> There are no error messages, no tripped breakers.  She has no issues with
> the system when she is there and leaves the system on.  Next weekend rolls
> around and she comes back out to find the inverter off again.  Schneider
> tech support seems to feel that the inverter is turning off on its own due
> to low battery voltage.  But there is nothing in the log that shown this.
> And there is a Ecogen 15KW installed to protect from ever seeing the low
> battery cut off.
>
> Has anyone experienced this?  My customer always comes ont on a friday and
> seems to believe the day of the week has something to do with this or this
> be cold induced?  It is rather pressing since winter is in full swing and a
> turned off inverter can mean frozen pipes.
>
> Any help out there?
>
> Aaron Mandelkorn
> President / Founder
> Renewable Energy Outfitters
> www.reosolar.com
> Off Grid Depot
> www.offgridnow.com
> 970-596-3744
>
>
>
>
> THE INFORMATION CONTAINED IN THIS E-MAIL MAY BE PRIVILEGED, CONFIDENTIAL,
> AND PROTECTED FROM DISCLOSURE. IF YOU ARE NOT THE INTENDED RECIPIENT, ANY
> DISSEMINATION, DISTRIBUTION, OR COPYING IS STRICTLY PROHIBITED.
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20191118/3eca1bb1/attachment.htm>


More information about the RE-Wrenches mailing list