Totally sounds like Low voltage disconnect to me.  Many, Many times the 
generator does not start when it should or connect to the inverter.  
I've had 2 systems recently, that both shut down, 1 had the LVD set 
really high, higher than the gen start, so that definitely didn't work.  
The next one would start the generator when required, but the generator 
voltage regulation was incorrect, so the inverter would never connect to 
it.  Thinking the Ecogen is going to save the day is going to be recipe 
for disaster;  over the years I've come to despise the Ecogen.  I'm 
seeing 50% failures, and some of the failures are catastrophic, complete 
engine failures.  I don't have a suggested replacement, other than go 
big enough (+20 kW) to get into the 1800 rpm water cooled equipment, or 
just get a decent portable.  At least with a portable, you can haul it 
in for service.

Ray Walters
Remote Solar
303 505-8760

On 11/18/19 8:00 PM, Aaron Mandelkorn wrote:
> This is a strange one.  I have a Schneider SW 4024 installed in a 
> remote area of Colorado.  Cold and high altitude.  Since the fall 
> every time my customer has gone out to her cabin she noticed that the 
> inverter is off.  She proceeded to turn the unit back on by pressing 
> the button on the SW. There are no error messages, no tripped 
> breakers.  She has no issues with the system when she is there and 
> leaves the system on.  Next weekend rolls around and she comes back 
> out to find the inverter off again.  Schneider tech support seems to 
> feel that the inverter is turning off on its own due to low battery 
> voltage.  But there is nothing in the log that shown this.  And there 
> is a Ecogen 15KW installed to protect from ever seeing the low battery 
> cut off.
>
> Has anyone experienced this?  My customer always comes ont on a friday 
> and seems to believe the day of the week has something to do with this 
> or this be cold induced?  It is rather pressing since winter is in 
> full swing and a turned off inverter can mean frozen pipes.
>
> Any help out there?
>
> Aaron Mandelkorn
> President / Founder
> Renewable Energy Outfitters
> www.reosolar.com <http://www.reosolar.com>
> Off Grid Depot
> www.offgridnow.com <http://www.offgridnow.com>
> 970-596-3744
>
>
>
>
> THE INFORMATION CONTAINED IN THIS E-MAIL MAY BE PRIVILEGED, 
> CONFIDENTIAL, AND PROTECTED FROM DISCLOSURE. IF YOU ARE NOT THE 
> INTENDED RECIPIENT, ANY DISSEMINATION, DISTRIBUTION, OR COPYING IS 
> STRICTLY PROHIBITED.
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20191118/717c9c5e/attachment.htm>


More information about the RE-Wrenches mailing list