[RE-wrenches] 30 amp disconnect/40 amp breaker
Greg
greg at remotepowerinc.com
Wed Aug 21 18:12:05 EDT 2019
Fellow Wrenches, I'm having a discussion with a utility engineer
regarding the following situation:
Installing a 6kW inverter that has a full rated output of 25 amps. 80%
of 30 is 24. That means to me I need to go up to a 40 amp breaker. I'm
running #8 (continuous load 25 x 1.25 etc.)
The engineer believes I should use a 60 amp disco since it's on a 40 amp
breaker. My thinking is I can use a 30 amp disco since it can not
produce more than 25 amps ever.
Do any of you have a reference that shows what I'm doing is okay? Not okay?
Thanks again,
Greg Egan
Remote Power Inc.