    Fellow Wrenches,  I'm having a discussion with a utility engineer
    regarding the following situation:<br>
    <br>
    Installing a 6kW inverter that has a full rated output of 25 amps. 
    80% of 30 is 24.  That means to me I need to go up to a 40 amp
    breaker.  I'm running #8 (continuous load 25 x 1.25 etc.)  <br>
    The engineer believes I should use a 60 amp disco since it's on a 40
    amp breaker.  My thinking is I can use a 30 amp disco since it can
    not produce more than 25 amps ever.  <br>
    <br>
    Do any of you have a reference that shows what I'm doing is okay?
    Not okay?  <br>
    <br>
    Thanks again, <br>
    Greg Egan<br>
    Remote Power Inc.  <br>