[RE-wrenches] 30 amp disconnect/40 amp breaker
Christopher Warfel
cwarfel at entech-engineering.com
Wed Aug 21 18:32:23 EDT 2019
Not going through the NEC, but it doesn't make sense to me to put in an
OCPD greater than the rating of the switch. I am sure you can find in
the spec sheet what the maximum OCPD allowed is. Chris
On 8/21/2019 6:12 PM, Greg wrote:
> Fellow Wrenches, I'm having a discussion with a utility engineer
> regarding the following situation:
>
> Installing a 6kW inverter that has a full rated output of 25 amps.
> 80% of 30 is 24. That means to me I need to go up to a 40 amp
> breaker. I'm running #8 (continuous load 25 x 1.25 etc.)
> The engineer believes I should use a 60 amp disco since it's on a 40
> amp breaker. My thinking is I can use a 30 amp disco since it can not
> produce more than 25 amps ever.
>
> Do any of you have a reference that shows what I'm doing is okay? Not
> okay?
>
> Thanks again,
> Greg Egan
> Remote Power Inc.
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190821/e415f7a9/attachment.htm>
More information about the RE-Wrenches
mailing list