[RE-wrenches] Physical of Electrical Interlock
Ray
ray at solarray.com
Tue Aug 13 14:30:17 EDT 2019
What amp rating do you need? Midnite Solar makes a small 30 amp manual
transfer switch, while Reliance (via Northern Tool) makes 60 and 100 amp
models. Or are you looking for automatic transfer? Generac makes a
bunch of 100 to 200 amp rated transfer switches. Square D and others
make some bigger load break rated stuff but it gets big and expensive.
Ray Walters
Remote Solar
303 505-8760
On 8/13/19 12:16 PM, Jon Siegenthaler wrote:
> Hello wrenchers,
> I have a client we're building for who is going to have installed two
> of the SolarEdge Storedge inverters with two of LG Chem RESU
> batteries. This electrical system also has a backup generator which
> then requires there to be an interlock between the inverters and the
> generator. I was hoping because this was a zero export system (as
> required or by punishment of paying the utility for your
> overproduction) that the SolarEdge smart meter would detect and not
> export to the generator, but as a fail-safe it would be better not to
> trust a $300 meter against a $10,000 generator and install an interlock.
>
> My question is; has anyone found an interlock that would work with
> this system? From my understanding the inverters would need to
> switched off, but then the dedicated panels that the inverters are
> powering would need to be transferred over to the generator power. The
> simplest answer I can come up with is a panel with no bussing (mounted
> on din rail) on one side with 4-2 pole breakers, each is set consists
> of 2-2 pole breakers with jumpers on the backside so that the inverter
> has a jumper to the dedicated load panel breaker. On the other side of
> the panel would be either on a bus or also with jumpers that went to
> 2-2 pole breakers for the generator in and out and then also the 2-2
> pole breakers for the dedicated load panels. Then there would be an
> interlock that slides from left to right to control which system was
> on, this being either PV or generator.
>
> Thanks ahead of time for any help or product suggestions,
>
> Jon Siegenthaler
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190813/dcd766b5/attachment.htm>
More information about the RE-Wrenches
mailing list