 Hello wrenchers,
I have a client we're building for who is going to have installed two of
the SolarEdge Storedge inverters with two of LG Chem RESU batteries. This
electrical system also has a backup generator which then requires there to
be an interlock between the inverters and the generator. I was hoping
because this was a zero export system (as required or by punishment of
paying the utility for your overproduction) that the SolarEdge smart meter
would detect and not export to the generator, but as a fail-safe it would
be better not to trust a $300 meter against a $10,000 generator and install
an interlock.

My question is; has anyone found an interlock that would work with this
system? From my understanding the inverters would need to switched off, but
then the dedicated panels that the inverters are powering would need to be
transferred over to the generator power. The simplest answer I can come up
with is a panel with no bussing (mounted on din rail) on one side with 4-2
pole breakers, each is set consists of 2-2 pole breakers with jumpers on
the backside so that the inverter has a jumper to the dedicated load panel
breaker. On the other side of the panel would be either on a bus or also
with jumpers that went to 2-2 pole breakers for the generator in and out
and then also the 2-2 pole breakers for the dedicated load panels. Then
there would be an interlock that slides from left to right to control which
system was on, this being either PV or generator.