    <p>What amp rating do you need?  Midnite Solar makes a small 30 amp
      manual transfer switch, while Reliance (via Northern Tool) makes
      60 and 100 amp models.  Or are you looking for automatic
      transfer?  Generac makes a bunch of 100 to 200 amp rated transfer
      switches.  Square D and others make some bigger load break rated
      stuff but it gets big and expensive.<br>
    </p>
    <pre class="moz-signature" cols="72">Ray Walters
Remote Solar
303 505-8760</pre>
    <div class="moz-cite-prefix">On 8/13/19 12:16 PM, Jon Siegenthaler
      wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CADLBWGXvO=g8Q_vrpDSMLZfkNRtKMrsBx0Wywy+fJ5iJNmPHrw@mail.gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div dir="ltr">
        <div>Hello wrenchers,</div>
        <div>I have a client we're building for who is going to have
          installed two of the SolarEdge Storedge inverters with two of
          LG Chem RESU batteries. This electrical system also has a
          backup generator which then requires there to be an interlock
          between the inverters and the generator. I was hoping because
          this was a zero export system (as required or by punishment of
          paying the utility for your overproduction) that the SolarEdge
          smart meter would detect and not export to the generator, but
          as a fail-safe it would be better not to trust a $300 meter
          against a $10,000 generator and install an interlock.<br>
          <br>
          My question is; has anyone found an interlock that would work
          with this system? From my understanding the inverters would
          need to switched off, but then the dedicated panels that the
          inverters are powering would need to be transferred over to
          the generator power. The simplest answer I can come up with is
          a panel with no bussing (mounted on din rail) on one side with
          4-2 pole breakers, each is set consists of 2-2 pole breakers
          with jumpers on the backside so that the inverter has a jumper
          to the dedicated load panel breaker. On the other side of the
          panel would be either on a bus or also with jumpers that went
          to 2-2 pole breakers for the generator in and out and then
          also the 2-2 pole breakers for the dedicated load panels. Then
          there would be an interlock that slides from left to right to
          control which system was on, this being either PV or
          generator. <br>
          <br>
          Thanks ahead of time for any help or product suggestions, <br>
        </div>
        <div><br>
        </div>
        <div>Jon Siegenthaler<br>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
  </body>
</html>