[RE-wrenches] To Bond or Not to Bond the Neutral to Ground
Jason Szumlanski
jason at floridasolardesigngroup.com
Thu Jul 25 11:29:13 EDT 2019
I think the answer is in 250.28(D)(2). A bonding jumper is required in each
service disconnect (including the solar disconnect) bonding neutral to
ground.
Then you have to look to 250.64(D) for how to run your GEC. There are
multiple ways to comply.
Consider 250.64(D)(3):
Think of a wiring enclosure with service laterals that has a bus bar for
neutral (as in multiple service disconnects for a property, regardless of
whether solar is present). Each service disconnect neutral connects to the
bus bar, but there is no GEC from each disconnect to the grounding
electrode. There is a single point on the bus bar in the service lateral
enclosure where the GEC connects and is routed to the grounding electrode
system. Each service disconnect requires a bonding jumper from neutral to
ground. But in that case you do not need to run a GEC from each service
disconnect bus bar to the service lateral bus bar. You only run the GEC
from a single disconnect or a single point on the common bus bar in the
service lateral enclosure. The neutral provides the EGC function/pathway
for each service disconnect. It might seem a little strange to NOT run a
EGC to each service disconnect, but that's the way I read it. So the single
common point of connection of the GEC can be in the existing service
disconnect and no GEC is required at all from the solar disconnect. The
bonding jumper is required to be installed in the solar disconnect.
But 250.64(D)(1) is the way we do it. Every jurisdiction around here
requires that a neutral and a ground (GEC) be run to each service
disconnect, including the solar disconnect and that the bonding jumper be
installed in the solar disconnect.
Another way I have seen it done that I DO NOT believe complies is to simply
pass through the solar neutral in the solar disconnect without landing it
there and just land it in the existing main service panel.
On Tue, Jul 23, 2019 at 4:39 PM Rick Brown <
rick at solshineenergyalternatives.com> wrote:
> Al,
> See 250.2:
> “Bonding Jumper, Supply-Side. A conductor installed on the supply side of
> a service or within a service equipment enclosure(s), or for a separately
> derived system, that ensures the required electrical conductivity between
> metal.”
>
> rick brown
> SolShine Energy Alternatives, LLC
> Electrical & Solar Contracting Services
> www.SolShineEnergyAlternatives.com
> Check, Virginia 24072
> 540.808.9502
>
> VA Class A Contractor Lic# 2705147660
> VA Master Electrician Lic# 2710062762
> VA Alternative Energy Systems Installer
> NABCEP Certified PV Installation Professional 110112-21
>
> On Jul 23, 2019, at 9:38 AM, Al Frishman <evolvedsolar at gmail.com> wrote:
>
> Hey Wrenchers,
> I have been having a design debate with several associates regarding
> bonding the Neutral to the Ground for Line Side grid connections.
>
> In the fused solar AC Disconnect located closest to the Service Line Side
> grid connection should the Neutral be bonded to Ground? What Article in
> the NEC defines the requirement.
>
> As always your feedback is appreciated.
>
> *Al Frishman*
> EvolvedSolar
> (917) 699-6641
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190725/a5a6a720/attachment.htm>
More information about the RE-Wrenches
mailing list