[RE-wrenches] To Bond or Not to Bond the Neutral to Ground

Rick Brown rick at solshineenergyalternatives.com
Tue Jul 23 16:39:35 EDT 2019


Al,
See 250.2:
“Bonding Jumper, Supply-Side. A conductor installed on the supply side of a service or within a service equipment enclosure(s), or for a separately derived system, that ensures the required electrical conductivity between metal.”

rick brown
SolShine Energy Alternatives, LLC
Electrical & Solar Contracting Services
www.SolShineEnergyAlternatives.com
Check, Virginia 24072
540.808.9502

VA Class A Contractor Lic# 2705147660
VA Master Electrician Lic# 2710062762
VA Alternative Energy Systems Installer  
NABCEP Certified PV Installation Professional 110112-21

> On Jul 23, 2019, at 9:38 AM, Al Frishman <evolvedsolar at gmail.com> wrote:
> 
> Hey Wrenchers,
> I have been having a design debate with several associates regarding bonding the Neutral to the Ground for Line Side grid connections.
> 
> In the fused solar AC Disconnect located closest to the Service Line Side grid connection should the Neutral be bonded to Ground?  What Article in the NEC defines the requirement.
> 
> As always your feedback is appreciated.
> 
> Al Frishman
> EvolvedSolar
> (917) 699-6641
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190723/cb627de7/attachment.htm>


More information about the RE-Wrenches mailing list