[RE-wrenches] Large Off-Grid Residential System and ciculating currents
William Miller
william at millersolar.com
Tue Jul 23 18:08:49 EDT 2019
Friends:
I am a complete newbie to any lithium technologies, so please forgive some
newbie questions:
I am used to working in amp hours. If we are looking for a battery bank in
the range of 100 kWh, this converts to about 2,083 amp/hours at 48 VDC. Is
my arithmetic correct? An on-line calculator seems to confirm this.
The biggest Blue Ion 2 battery is 16 kwh. At 48 VDC this is about 333
amp/hours. This is like an L16. To get 100 kwh you would need to parallel
6 strings of the 16 kWh batteries. I would never do this with L-16s. Is
anyone worried about circulating currents in this type of installation? Is
there technology to prevent one string from cannibalizing another?
Here is another, more academic question below:
In case I am using a term I made up (which is often the case), I define
circulating currents as currents flowing between parallel strings without
any outside influence. For example, if you disconnected all charging and
loads from an array with two parallel strings, unless the strings were
absolutely identical in electrical characteristics, there would be some
current flowing between the two strings. In my opinion this is the
Achilles heel in parallel strings. Also my opinions: 2. The more strings
you have the more chance there will be debilitating circulating currents.
3. The older the batteries, the more the electrical characteristics will
vary and the more likely you will get higher circulating currents.
It is my theory that if you can measure the circulating currents, or the
difference between parallel battery strings at any point in the operation
of same, you can get a read on the health of the strings. The more the
operating or idle currents diverge, the more one string will discharge the
other string. I guess this is some part of a battery management system. I
am guessing for the Blue Ion 2 to work in 6 parallel strings, they need to
monitor and control this difference in currents.
We just installed a flooded battery array (2 strings of 4 Deka M6100-33
batteries). My plan is to retrofit the installation with a 1000A/100mv
shunt in the negative leads of both strings. With a DVM I can spot check
the circulating currents to learn about the battery health. In fact I have
a remote monitoring system
<https://millersolar.com/MillerSolar/Portfolio/Commercial/Cal_Trans/Remote/Remote_Control.html>
with some spare ports that can log these values. Might be an interesting
experiment.
I appreciate any input on the viability of the Blue Ion 2 or other small
battery systems in multi-string installations. My customers are asking for
new technology, but I instinctively avoid parallel battery strings.
William Miller
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
Quote of the month: “As they age, batteries transition from energy
storage devices to energy consuming devices.“ W. Miller
*From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
Behalf Of *Lou Russo
*Sent:* Saturday, July 20, 2019 1:50 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Large Off-Grid Residential System
Blue Ion 2.0 with Outback or SMA. Works every time.
Blue Planet's tech support is great, the warranty is even better.
Aloha,
Lou Russo
lou at spreesolarsystems.com
808 345 6762
Spree Solar Systems LLC
CT-34322
On Sat, Jul 20, 2019 at 10:36 AM Jay <jay.peltz at gmail.com> wrote:
Hi Marco,
Is the max surge 7kw, which is what is listed on line?
Jay
Peltz Power
On Jul 19, 2019, at 3:10 PM, Marco Mangelsdorf <marco at pvthawaii.com> wrote:
Seven to eight Tesla Powerwalls will get you that assuming that the service
entrance is no bigger than 200A.
marco
On Friday, July 19, 2019, Jason Szumlanski <
jason at floridasolardesigngroup.com> wrote:
What are current popular options for battery based systems in the 100kWh
range? Preferably Lithium.
Also, what inverter pairing is suggested with total stacked capacity of
36kW, 120/240V?
This is slightly larger than some of the systems I have worked with
recently. I'm a bit out of the loop, particularly on the battery side of
things.
Jason Szumlanski
Florida Solar Design Group
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190723/5bea6304/attachment.htm>
More information about the RE-Wrenches
mailing list