[RE-wrenches] Bus bar battery jumpers
drake.chamberlin at redwoodalliance.org
drake.chamberlin at redwoodalliance.org
Wed May 1 08:05:49 EDT 2019
Glenn,
Thank you for that good information.
Where do you find the specifications relating cross sectional area to
amperage? Section 366.23 of the NEC allows 1000 A / sq. in. of cross
sectional area of the conductor. Is that a good rule of thumb, or is
there something more specific to battery busing?
Drake
----- Original Message -----
From: glenn.burt at glbcc.com "RE-wrenches"
<re-wrenches at lists.re-wrenches.org>
To:"RE-wrenches" <re-wrenches at lists.re-wrenches.org>
Cc:
Sent:Tue, 30 Apr 2019 20:31:39 -0400
Subject:Re: [RE-wrenches] Bus bar battery jumpers
I have always bought the appropriately sized for the anticipated
current, copper bar stock from McMaster Carr and cut, drilled and
applied heat shrink myself…
-Glenn
FROM: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> ON
BEHALF OF Drake
SENT: Tuesday, April 30, 2019 12:27 PM
TO: RE-wrenches <re-wrenches at lists.re-wrenches.org>
SUBJECT: [RE-wrenches] Bus bar battery jumpers
Hello Wrenches,
I am wiring a set of 2 V Concorde batteries for 48 V. Each battery has
2 terminals which will be about 2 1/2 inches away from the terminals
they will be wired to. Standard battery jumpers would be ridiculous in
this situation. Busbars would be clean and efficient. Concorde doesn't
have a solution.
Does anyone know of a source for busbars?
Thank you,
Drake
Drake Chamberlin
Athens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV
740-448-7328
http://athens-electric.com/ [1]
Links:
------
[1] http://athens-electric.com/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190501/23e2b8d1/attachment.htm>
More information about the RE-Wrenches
mailing list