[RE-wrenches] Bus bar battery jumpers
Bill Hennessy
bill at berkssolar.com
Wed May 1 09:32:38 EDT 2019
table 3 is a bus bar size selector based on ampacities--you can match that with what Mcmaster offers in 101 copper (higher purity than standard 110 copper).we've made bus bars for years using this method. trickiest part is drilling a clean hole in the copper.
https://www.copper.org/publications/pub_list/pdf/a6022.pdf
Bill Hennessy
Berks Solar, LLC
371 Centennial Rd
Mertztown, PA 19539
o 610 682 4300
c 484 560 4666
NABCEP certified installer
PA contractor #44411
www.berkssolar.com
On Wednesday, May 1, 2019, 8:05:59 AM EDT, drake.chamberlin at redwoodalliance.org <drake.chamberlin at redwoodalliance.org> wrote:
Glenn,
Thank you for that good information.
Where do you find the specifications relating cross sectional area to amperage? Section 366.23 of the NEC allows 1000 A / sq. in. of cross sectional area of the conductor. Is that a good rule of thumb, or is there something more specific to battery busing?
Drake
----- Original Message -----
From: glenn.burt at glbcc.com "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
To:"RE-wrenches" <re-wrenches at lists.re-wrenches.org>
Cc:
Sent:Tue, 30 Apr 2019 20:31:39 -0400
Subject:Re: [RE-wrenches] Bus bar battery jumpers
I have always bought the appropriately sized for the anticipated current, copper bar stock from McMaster Carr and cut, drilled and applied heat shrink myself…
-Glenn
From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of Drake
Sent: Tuesday, April 30, 2019 12:27 PM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Subject: [RE-wrenches] Bus bar battery jumpers
Hello Wrenches,
I am wiring a set of 2 V Concorde batteries for 48 V. Each battery has 2 terminals which will be about 2 1/2 inches away from the terminals they will be wired to. Standard battery jumpers would be ridiculous in this situation. Busbars would be clean and efficient. Concorde doesn't have a solution.
Does anyone know of a source for busbars?
Thank you,
Drake
Drake Chamberlin
Athens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV
740-448-7328
http://athens-electric.com/
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190501/8dcbe094/attachment.htm>
More information about the RE-Wrenches
mailing list