It looks to me the Radian is speced at max altitude of 6,561 feet. I
have asked Schneider about the XW series and they agree that there is not
anything they can find that spells this out. The 2 different Schneider
charge controllers are speced at 6,500 feet.
So for warranty required
situations that is what I can find. More later.
Dave Angelini Offgrid
Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
[1]
e-mail offgridsolar at sti.net [2]
text 209 813 0060
On Fri, 12 Apr 2019
19:13:37 +0000, Lones Tuss wrote:
Hello All
Outback's Product
Warranty is not based or negated by the altitude of the installation.
Altitude ratings ensure full spec operation of the equipment up to the
stated elevation . As noted in several posts due to thinner air cooling of
equipment can be affected. Additional cooling may be required and or
additional products to achieve the necessary load requirements.
FROM:
RE-wrenches ON BEHALF OF jerrysgarage01
SENT: Friday, April 12, 2019
11:26 AM
TO: RE-wrenches
SUBJECT: Re: [RE-wrenches] High altitude
off-grid systems
Wrenches
Here is the math, well the answer at sea
level your body has 14.70 PSI exerted on it, at 10,000 feet you only have
10.163 PSI, reduced air pressure, reduced cooling or heating ability
adjusted for standard sea level temp or just over 69%.
I have done work
in Hawaii on the big island up at the summit, it can be warm and very thin
air, without air to cool no inverter will perform very well. I have some
SMA, FX and Raidians in warm high altitude locations and added extra
cooling to compensate for the lack of air. You will hear the cooling fans
spinning faster, moving less air at higher altitudes.
SMA sunny island
does have a 9k plus operating altitude but de-rates at less the 7k.
Jerry
PV inspector
Sent from my Verizon, Samsung Galaxy
smartphone
-------- Original message --------
From: Jay Pozner
Date: 4/12/19 10:06 AM (GMT-08:00)
To: RE-wrenches
Subject:
Re: [RE-wrenches] High altitude off-grid systems
We do a fair amount
of systems at "altitude". Recently we had an issue with a Radian system at
about 10,000'. An 8048 inverter screaming (fans running hard) with just
2000 watts of load. I hounded tech support for two years, and even after
switching power modules, etc in the end the techs claim a fairly
substantial deration (that I can't quote right now) of inverter performance
because of cooling issues. We ultimately added another inverter to the
system at the end of last summer. I hope this season we will see a better
result. It makes sense, given the difference in air density, but I do
scratch my head and wonder why we haven't seen such issues with the older
FX's, and some of the older legacy systems?
I also know that the Midnite
classic charge controllers seem to run the fans quite hard as well. I
haven't had to replace any of the fans, and the controllers are performing
great, but wonder if that will be an issue in the future. It would be great
if some manufactures would give us a quality, competitively priced,
equipment that is rated for altitude, but I don't think there are that many
options out there as of now
.
Jay Pozner
(970) 642-5554
www.nunatakenergy.com [5]
NABCEP Certified PV Installer:
Cert.#031310-177
On Fri, Apr 12, 2019 at 9:17 AM Steve Higgins wrote:
Not to add
fuel to the fire... and it's been almost 7 years since I've been with an
Inverter manufacturer so here is my .02 cents... So again, I hope I'm not
overstepping the boundaries of the Wrenches list.
If I remember
correctly the main issue with the high altitude installs are some of the
components that are used to build the inverter/controllers aren't rated to
be used at high altitude, one of the main components that have this issue
is the electrolytic capacitors. Of course, the specs vary from component to
component. I've seen some rated as low as 8000 ft to some as rated as high
as 30,000 ft. It really just depends on the part(s) that the manufacturer
used to build the product.
As you gain altitude the temperatures and
the air pressure decrease, as it was explained to me years ago the problem
is with the temperature decrease, this will affect the capacitance of the
capacitor. The colder temps will reduce the overall capacitance of the
capacitor, just like it will with a battery.
These caps are generally
used to filter noise from circuits, so when these fail, or the capacitance
values fall, you don't get the filtering you need and this induces noise
into your circuitry possibly causing overall failure or worse, the dreaded
intermittent failure. Generally, if the inverters/controllers are kept on
and warm, you won't have too many problems, it's when they are in extremely
cold temperatures is when you will start having issues.
Hope this
helps! Have a good weekend!
[7]
STEVE HIGGINS â‹…TECHNICAL SERVICES
MANAGER
T+1.902.597.4020 M+1.206.790.5840
F+1.902.597.8447 E
steve at surrette.com [8]
[9] [10] [11] [12] [13]
-------------------------
CONFIDENTIALITY: The information transmitted
herein is intended only for the addressee and may contain confidential,
proprietary and/or privileged material. Any unauthorized review,
distribution or other use of or the taking of any action in reliance upon
this information is prohibited. If you receive this email in error, please
contact the sender and delete or destroy this message and all copies.
-------------------------
On Fri, Apr 12, 2019 at 7:47 AM wrote:
Folks:
The issue here ulltimately isn't whether it works or not, it's
if it's WARRANTED. Some purchasers (in this case the USFS) mandate that all
equipment be warranted for high altitudes. And that leaves out several
major suppliers.
Chris Daum
Oasis Montana Inc.
FROM: RE-wrenches ON
BEHALF OF Ray
SENT: Thursday, April 11, 2019 10:55 PM
TO:
re-wrenches at lists.re-wrenches.org [16]
SUBJECT: Re: [RE-wrenches] High
altitude off-grid systems
We've had some systems at 11,000 ft plus, for
almost 20 years. We have mixtures of Outback, Midnite, Blue Sky, and old
Trace equipment. Never any issues with electronics related to altitude.
Actually the altitude related system issues are generator derating, and
array output exceeding STC ratings on really clear cold days due to the
thin atmosphere. The third issue would be installers not being able to
catch our breath after jogging back to the truck.
Ray Walters
Remote
Solar
303 505-8760
On 4/11/19 3:39 PM, Dan Fink wrote:
Hi Chris; I
am deeply concerned about this as nearly 100% of the systems I install are
at 8000 ft (2500m) or higher. I've never had a problem with warranty claims
to Outback or Schneider up to this time. If this is a "new thing" I'd
really like to know about it, on list or off.
The alitude de-rate stuff
seems to involve dialectric ratings on the transformer coils, and low air
density for cooling. I think that's all in ANSI.
Dan Fink
Director
of Solar Education, Greendustrial Training LLC
IREC Certified
Instructor(tm) for:
~ PV Installation Professional
~ Small Wind
Installer
NABCEP PV Associate
Executive Director, Buckville Energy
Consulting
NABCEP Registered Continuing Education Providers
dan.fink at greendustrialtraining.com [17]
970-672-4342
On Thu, Apr
11, 2019 at 1:28 PM wrote:
Hi folks:
I am curious as to how many
of you sell/install battery/inverter systems at high altitudes? Have you
had any particular issues with them? Last year we discovered (in a mostly
costly fashion) that Schneider inverters (and also Outback) are not
warranted above 6500 ft.
Magnum inverters are warranted to 15,000 ft max
altitude.
Best,
Chris Daum
Oasis Montana Inc.
406-777-4309 or 4321
406-777-4309 fax
www.oasismontana.com [19]
_______________________________________________
List sponsored by
Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org [20]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org [21]
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[22]
List rules ">_______________________________________________
List
sponsored by Redwood Alliance
List Address:
RE-wrenches at lists.re-wrenches.org [25]
Change listserver email address
">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[26]
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[27]
List rules ">www.re-wrenches.org/etiquette.htm [28]
Check out or
update participant bios:
www.members.re-wrenches.org
[29]
_______________________________________________
List sponsored by
Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org [30]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org [31]
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[32]
List rules & etiquette:
www.re-wrenches.org/etiquette.htm [33]
Check out or update participant bios:
www.members.re-wrenches.org [34]
_______________________________________________
List sponsored by
Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org [35]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org [36]
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[37]
List rules & etiquette:
www.re-wrenches.org/etiquette.htm [38]
Check out or update participant bios:
www.members.re-wrenches.org [39]
--
Links:
------
[1] http://members.sti.net/offgridsolar/
[2]
mailto:offgridsolar at sti.net
[3] mailto:jay at nunatakenergy.com
[4]
mailto:re-wrenches at lists.re-wrenches.org
[5]
http://www.nunatakenergy.com/
[6] mailto:steve at surrette.com
[7]
http://www.rollsbattery.com
[8] mailto:steve at surrette.com
[9]
http://www.facebook.com/RollsBattery
[10]
http://www.twitter.com/RollsBattery
[11]
https://www.youtube.com/user/RollsBattery
[12]
https://www.linkedin.com/company/rolls-battery-engineering
[13]
http://www.instagram.com/RollsBattery
[14]
mailto:chris at oasismontana.com
[15]
mailto:re-wrenches-bounces at lists.re-wrenches.org
[16]
mailto:re-wrenches at lists.re-wrenches.org
[17]
mailto:dan.fink at greendustrialtraining.com
[18]
mailto:chris at oasismontana.com
[19] http://www.oasismontana.com
[20]
mailto:RE-wrenches at lists.re-wrenches.org
[21]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[22]
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[23]
http://www.re-wrenches.org/etiquette.htm
[24]
http://www.members.re-wrenches.org
[25]
mailto:RE-wrenches at lists.re-wrenches.org
[26]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[27]
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[28]
http://www.re-wrenches.org/etiquette.htm
[29]
http://www.members.re-wrenches.org
[30]
mailto:RE-wrenches at lists.re-wrenches.org
[31]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[32]
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[33]
http://www.re-wrenches.org/etiquette.htm
[34]
http://www.members.re-wrenches.org
[35]
mailto:RE-wrenches at lists.re-wrenches.org
[36]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[37]
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[38]
http://www.re-wrenches.org/etiquette.htm
[39]
http://www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190416/7ac29398/attachment.htm>
More information about the RE-Wrenches
mailing list