I had that problem with an older XW and problem was corrupted firmware. It
took many years to get Schneider to admit that the problem was not my
installation or programming.
New firmware fixed a nagging problem of runaway voltage and destroyed
batteries. I also had found that resetting to factory defaults was causing
some of the problem as the default for absorb was 6 hours instead of the
one hour I or less that it should have been. Found that problem by
resetting to factory defaults and then checking every setting. With the bad
firmware I was seeing the charge rate and voltage setpoints totally ignored
and saw battery go up to 67 volts!
John Blittersdorf
On Mon, Mar 25, 2019 at 4:35 PM Jason Szumlanski <
jason at floridasolardesigngroup.com> wrote:
> I have four inverter/chargers (master and 3 slaves) that are blowing past
> their 57.6V setpoint that I programmed and confirmed via the Context
> Combox. They are hitting 58.4V and tripping the battery management units on
> a set of Lithium Batts. Any ideas why this would happen? I can disable
> chargers on individual units, so I know the settings are getting uploaded
> via the Combox.
>
> Jason Szumlanski
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190326/fc9e5a54/attachment.htm>
More information about the RE-Wrenches
mailing list