[RE-wrenches] Xantrex XW6048 (quad) blowing past setpoints

Jason Szumlanski jason at floridasolardesigngroup.com
Wed Mar 27 11:34:17 EDT 2019


Fortunately there are battery management systems for the parallel banks
that are a failsafe, but the nuisance tripping is unacceptable and does not
allow for an absorption time.

Maybe I have the same issue... I have never updated an XW firmware before.
I'll have to look into that.




On Tue, Mar 26, 2019 at 9:27 AM John Blittersdorf <
john.blittersdorf at gmail.com> wrote:

> Jason.
> I had that problem with an older XW and problem was corrupted firmware.
> It took many years to get Schneider to admit that the problem was not my
> installation or programming.
> New firmware fixed a nagging problem of runaway voltage and destroyed
> batteries. I also had found that resetting to factory defaults was causing
> some of the problem as the default for absorb was 6 hours instead of the
> one hour I or less that it should have been.  Found that problem by
> resetting to factory defaults and then checking every setting. With the bad
> firmware I was seeing the charge rate and voltage setpoints totally ignored
> and saw battery go up to 67 volts!
>
> John Blittersdorf
>
>
> On Mon, Mar 25, 2019 at 4:35 PM Jason Szumlanski <
> jason at floridasolardesigngroup.com> wrote:
>
>> I have four inverter/chargers (master and 3 slaves) that are blowing past
>> their 57.6V setpoint that I programmed and confirmed via the Context
>> Combox. They are hitting 58.4V and tripping the battery management units on
>> a set of Lithium Batts. Any ideas why this would happen? I can disable
>> chargers on individual units, so I know the settings are getting uploaded
>> via the Combox.
>>
>> Jason Szumlanski
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/35885b2b9e57b6eb01c183fbc56993dc5f3bd891?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=2a2ddcfb94f2d451>
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> <https://mailtrack.io/trace/link/a219cf0c009d8b3ca24b626574f3ffab2b646351?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=5677a283806778f3>
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> <https://mailtrack.io/trace/link/e9694af95a2a73dfd5f4ae4de88f7fb84d833c76?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=ece84064ed4c8d7b>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> <https://mailtrack.io/trace/link/6eedc58e3b4f642963d86cdf7fa72b73d2b6522d?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=47c5444e95cc8aec>
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/d9e145a3adb77b320f4010085738860f893f9dfa?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=f906246ee60a56e2>
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> <https://mailtrack.io/trace/link/8205755d96c5afc268fce0df2db76d0995e8b585?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=18ced733fb9dca92>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/963d00b7ae1bf2d0bbbd19e65b4a031c70349f09?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=fed59fdfd7680f34>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/30b778c386023e33bb6b5d218a3356f017818374?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=8d223077483d8703>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190327/f28de5c8/attachment.htm>


More information about the RE-Wrenches mailing list