[RE-wrenches] Magnum inverter issue
Jerry Shafer
jerrysgarage01 at gmail.com
Thu Dec 13 00:20:18 EST 2018
Wrenches
I can only use Outback as a reference, is the programming set to search not
on,
What happens under a light load, l have seen cycling on Outbacks that had
low idle load and were programmed to high and they hunted like that.
Jerry
On Wed, Dec 12, 2018, 7:16 PM Jay <jay.peltz at gmail.com wrote:
> Hi all,
>
> I’ve had the following issue with a new PAE 4024.
>
> It’s ac voltage will rise and fall about 10+ volts ( 124-115) over about
> 10 seconds like clock work. Regardless of the load, or battery SOC/voltage.
> I checked with a local shop, they also have the issue. They checked all
> their back stock and they all did the same thing. However they had an older
> one, say 6 months old that didn’t do it. Nor do any of my previous magnum
> installs do this.
>
> Clients are not too thrilled with this as lights go up and down in
> brightness.
>
> Magnum’s response was that this is normal for an off grid inverter and
> that somehow this “feature” has to do with it being able to AC couple
> better.
>
> I’m writing to ask if others have seen this as well and more importantly
> if anyone has a fix?
>
> Thanks,
>
> Jay
> Peltz Power
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20181212/37ca5590/attachment.htm>
More information about the RE-Wrenches
mailing list