[RE-wrenches] Mate 3 shutdown

Chris Mason cometenergysystems at gmail.com
Thu Oct 11 07:20:46 EDT 2018


Outback has been good at sending a crossover replacement, meaning the new
one arrives then you send back the old one. The MATE3 has problems, I have
replaced one twice.

On Wed, Oct 10, 2018 at 9:30 PM Jay <jay.peltz at gmail.com> wrote:

> Hi Dana,
>
> If you look at the graphs, are they smooth or really kind of unclear ?
>
> How often do you clear the internal data?
>
> The mate 3 has a fatal flaw. Th internal data will over write code once
> memory is full.
>
> One indicator is locking up, another is the graphs looking unclear.
>
> It’s recommended to clear it at least every 6 months.
>
> And even with current firmware and clearing memory, I still see it happen.
>
> Jay
>
>
>
>
>
>
> On Oct 10, 2018, at 4:51 PM, Dana <Dana at solarwork.com> wrote:
>
> My learned fellow Sparkies,
>
>
>
> I have at home off-grid Radian with Mate 3 monitor. Periodically &
> randomly my Mate 3 blanks out and requires a reboot (un-plug / re-plug).
> While this is not such a big deal to address, the total loss of ALL the
> performance & usage data is really concerning in the event that I need the
> data for a T/S.
>
>
>
> I have not called OB as there is no cell service at or near the system and
> to do so is a huge time killer back & forth & waiting to check again. I am
> convinced the brain trust here is the answer.
>
>
>
> Has anyone else experienced this?
>
> Any remedial action to correct this issue?
>
>
>
> Let me know & thanks.
>
>
>
>
> ----------------------------------------------------------------------------
>
> Dana Orzel                                           NABCEP # 051112-136
>
> Cell - 208.721.7003                     Email - dana at solarwork.com
>
> Great Solar Works, Idaho Inc                    www.solarwork.biz
>
> ID PV Contractor - # 028765 -         ID PV Electrician # 028374
>
> "Responsible Technologies for Responsible People since 1988"
>
> Please consider the environment before printing this email.
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 
Chris Mason
NABCEP Certified Solar PV Installerâ„¢
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20181011/0d44d9fa/attachment.htm>


More information about the RE-Wrenches mailing list