[RE-wrenches] Surge arrestors on strings
Drake
drake.chamberlin at redwoodalliance.org
Tue Oct 9 17:02:32 EDT 2018
Hi boB,
I will keep putting an SPD on each string and on the AC line.
Sometimes my systems end up with a lot of blue lights hanging from a
wiring gutter!
Have you ever heard of any problems using the Midnite SPDs with Sunny
Boy TL series inverters? So far, I don't think I've had a problem,
although one TL-22, on a large metal roof, had arc fault protector trips.
Thanks,
Drake
Drake Chamberlin
Athens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV
740-448-7328
<http://athens-electric.com/>http://athens-electric.com/
At 01:39 PM 10/9/2018, you wrote:
>Content-Type: multipart/alternative;
> boundary="------------98C0DCEF93B9ECF248E0580B"
>Content-Language: en-US
>
>
>For an inverter with two MPPT inputs, you will need to treat the
>negatives and positive lines separate unless
>the manufacturer says something else. That means one SPD per array
>unfortunately. Negative and positive connect
>to separate leads of the SPD and then ground in the middle. As both
>positive and negative PV lines rise together
>relative to ground, the SPD is supposed to clamp that rise to below
>the equipment's hi-pot voltage that they test
>to at the factory. (i.e. common mode voltage rise) All wires except
>for ground (chassis) of the equipment are tied
>together and the hi-pot machine (sort of like a Megger ?) applies
>the high voltage between all those wires on one
>side and ground on the other to make sure the insulation doesn't
>break down inside the equipment.
>This hi-pot test goes for AC utility input/output connections and
>DC from the PV input side.
>
>The SPD has to clamp plus and minus and AC inputs to a lower
>voltage than this hipot rating but higher voltage
>than lines will see differentially in voltage. Remember that in a
>3-wire SPD, there is two sets of MOVs in series and
>the center is tied to ground. If one MOV starts conducting at say,
>500 volts DC then you can apply up to 1000
>volts between the hot leads. Each plus and negative line can rise
>up to 500 volts from the lightning before they
>start to clamp. The bigger the lightning strikes effect, the more
>current will be applied to the MOVs though and
>the clamp voltage will rise somewhat. That's why the SPD arrestor
>voltage should be well below the hi-pot voltage,
>whatever that is... Hi-pot voltages are quite a bit higher than the
>operating voltage. For example, All Classic CC's
>are tested to 2270 volts DC from hot lines to ground. It's
>something like double the operating voltage plus 1000V
>and multiply by 1.414 for DC rating..... I'm going off memory so
>don't quote me on that but something like that.
>
>I think that Ray has the right idea about short connections like
>from the local generator. Battery also.
>Just apply SPDs to anything that goes outside like an antenna.
>
>boB
>
>
>On 10/9/2018 8:26 AM, cwarfel wrote:
>>
>>I think something on the order of 90+% lightning strikes come from
>>the utility feed, not the dc side. That has to be ignored if in a
>>high strike area or grid isolated.
>>
>>On 10/8/2018 10:37 PM, Ray wrote:
>>>
>>>I believe you can use the SPD 300 AC on 2 strings, if PV neg is
>>>grounded. You would connect the green to ground (or PV neg) and
>>>then connect the red to one string pos, and connect the black to
>>>the other string pos. This would be limited to 300 v also. I
>>>haven't tried that exact configuration, but I have used the 300 AC
>>>to protect both the AC in and AC out on 120 vac inverters. I also
>>>believe you can use a 600 DC version, and wire as I mentioned, but
>>>the LEDs won't light. If you are using ungrounded inverters, then
>>>I think you would need an SPD for each string in order to protect
>>>both the pos and neg of each string, like you've been doing.
>>>
>>>Maybe someone from Midnite can clarify this.
>>>
>>>As far as it being worth it, I haven't had lightning related
>>>damage since I started using the Midnite SPDs, and I used to have
>>>system damage every year. If you are not in lightning country, or
>>>the install is in a low spot with less likelihood of taking a hit,
>>>you might be able to skimp. But for some of these off grid ridge
>>>top installs, I consider it a must. Some times I don't install one
>>>on the gen circuit, if its really close.
>>>
>>>
>>>
>>>Ray Walters
>>>Remote Solar
>>>303 505-8760On 10/8/18 4:03 PM, Drake wrote:
>>>>Hello Wrenches,
>>>>
>>>>Do you use surge arrestors with multi MPPT input string
>>>>inverters? Do you put a separate arrestor on each MPPT input? I
>>>>find it sort of pricey using a Midnite Solar arrestor on each
>>>>string, but have been doing that. Is there a less expensive
>>>>approach that is effective?
>>>>
>>>>I believe the Midnite units are the best. Are they worth the expense?
>>>>
>>>>Thank you,
>>>>
>>>>Drake
>>>>
>>>>
>>>>Drake Chamberlin
>>>>Athens Electric LLC
>>>>OH License 44810
>>>>CO License 3773
>>>>NABCEP Certified Solar PV
>>>>740-448-7328
>>>><http://athens-electric.com/>http://athens-electric.com/
>>>>
>>>>
>>>>
>>>>
>>>>_______________________________________________
>>>>List sponsored by Redwood Alliance
>>>>
>>>>List Address:
>>>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>>>
>>>>Change listserver email address & settings:
>>>><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>>List-Archive:
>>>><http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>
>>>>List rules & etiquette:
>>>><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>>>>
>>>>Check out or update participant bios:
>>>><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>>>>
>>>
>>>
>>>
>>>
>>>_______________________________________________
>>>List sponsored by Redwood Alliance
>>>
>>>List Address:
>>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>>
>>>Change listserver email address & settings:
>>><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>>List-Archive:
>>><http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>>List rules & etiquette:
>>><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>>>
>>>Check out or update participant bios:
>>><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>>>
>>
>>--
>>
>> Christopher Warfel, PE
>> ENTECH Engineering, Inc.
>>PO Box 871, Block Island, RI 02807
>> (401)466-8978
>>
>><http://entech-engineering.com>
>>EEI logo
>>
>>
>>
>>
>>_______________________________________________
>>List sponsored by Redwood Alliance
>>
>>List Address:
>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>
>>Change listserver email address & settings:
>><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>List-Archive:
>><http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>>List rules & etiquette:
>><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>>
>>Check out or update participant bios:
>><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>>
>
>
>
>_______________________________________________
>List sponsored by Redwood Alliance
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Change listserver email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out or update participant bios:
>www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20181009/85dfab8c/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 2f77d532.jpg
Type: image/jpeg
Size: 17117 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20181009/85dfab8c/attachment.jpg>
More information about the RE-Wrenches
mailing list