[RE-wrenches] Surge arrestors on strings

Bill Battagin frenergy at psln.com
Tue Oct 9 18:05:35 EDT 2018


boB,

             To add to Drake's  wonderings, I've had a few SMA TL-40 
inverters trip with an AFCI fault.  Significant hassle to get onsite and 
deal with it. Some with metal roofs some without, may have been 
lightening in the area.

Bill


On 10/9/2018 2:02 PM, Drake wrote:
> Hi boB,
>
> I will keep putting an SPD on each string and on the AC line. 
> Sometimes my systems end up with a lot of blue lights hanging from a 
> wiring gutter!
>
> Have you ever heard of any problems using the Midnite SPDs with Sunny 
> Boy TL series inverters? So far, I don't think I've had a problem, 
> although one TL-22, on a large metal roof, had arc fault protector trips.
>
> Thanks,
>
> Drake
>
> Drake Chamberlin
> /Athens Electric LLC
> OH License 44810
> CO License 3773
> NABCEP Certified Solar PV
> 740-448-7328
> /http://athens-electric.com/
>
>
>
> At 01:39 PM 10/9/2018, you wrote:
>> Content-Type: multipart/alternative;
>>  boundary="------------98C0DCEF93B9ECF248E0580B"
>> Content-Language: en-US
>>
>>
>> For an inverter with two MPPT inputs, you will need to treat the 
>> negatives and positive lines separate unless
>> the manufacturer says something else.  That means one  SPD per array 
>> unfortunately.  Negative and positive connect
>> to separate leads of the SPD and then ground in the middle.  As both 
>> positive and negative PV lines rise together
>> relative to ground, the SPD is supposed to clamp that rise to below 
>> the equipment's hi-pot voltage that they test
>> to at the factory.  (i.e. common mode voltage rise) All wires except 
>> for ground (chassis) of the equipment are tied
>> together and the hi-pot machine (sort of like a Megger ?) applies the 
>> high voltage between all those wires on one
>> side and ground on the other to make sure the insulation doesn't 
>> break down inside the equipment.
>> This hi-pot test goes for AC  utility input/output connections and DC 
>> from the PV input side.
>>
>> The SPD  has to clamp plus and minus and AC inputs to a lower voltage 
>> than this hipot rating but higher voltage
>> than lines will see differentially in voltage.  Remember that in a 
>> 3-wire SPD, there is two sets of MOVs in series and
>> the center is tied to ground.  If one MOV starts conducting at say, 
>> 500 volts DC then you can apply up to 1000
>> volts  between the hot leads.  Each plus and negative line can rise 
>> up to 500 volts from the lightning before they
>> start to clamp.  The  bigger the lightning strikes effect, the more 
>> current will be applied to the MOVs though and
>> the clamp voltage will rise somewhat.  That's why the SPD arrestor 
>> voltage should be well below the hi-pot voltage,
>> whatever that is...  Hi-pot voltages are quite a bit higher than the 
>> operating voltage.  For example, All Classic CC's
>> are tested to 2270 volts DC from hot lines to ground.  It's something 
>> like double the operating voltage plus 1000V
>> and multiply by 1.414 for DC rating.....  I'm going off memory so 
>> don't quote me on that but something like that.
>>
>> I think that Ray has the right idea about short connections like from 
>> the local generator.  Battery also.
>> Just apply SPDs to anything that goes outside like an antenna.
>>
>> boB
>>
>>
>> On 10/9/2018 8:26 AM, cwarfel wrote:
>>>
>>> I think something on the order of 90+% lightning strikes come from 
>>> the utility feed, not the dc side. That has to be ignored if in a 
>>> high strike area or grid isolated.
>>>
>>> On 10/8/2018 10:37 PM, Ray wrote:
>>>>
>>>> I believe you can use the SPD 300 AC on 2 strings, if PV neg is 
>>>> grounded.  You would connect the green to ground (or PV neg) and 
>>>> then connect the red to one string pos, and connect the black to 
>>>> the other string pos.  This would be limited to 300 v also.  I 
>>>> haven't tried that exact configuration, but I have used the 300 AC 
>>>> to protect both the AC in and AC out on 120 vac inverters.  I also 
>>>> believe you can use a 600 DC version, and wire as I mentioned, but 
>>>> the LEDs won't light. If you are using ungrounded inverters, then I 
>>>> think you would need an SPD for each string in order to protect 
>>>> both the pos and neg of each string, like you've been doing.
>>>>
>>>> Maybe someone from Midnite can clarify this.
>>>>
>>>> As far as it being worth it, I haven't had lightning related damage 
>>>> since I started using the Midnite SPDs, and I used to have system 
>>>> damage every year.  If you are not in lightning country, or the 
>>>> install is in a low spot with less likelihood of taking a hit, you 
>>>> might be able to skimp.  But for some of these off grid ridge top 
>>>> installs, I consider it a must. Some times I don't install one on 
>>>> the gen circuit, if its really close.
>>>>
>>>>
>>>>
>>>> Ray Walters
>>>> Remote Solar
>>>> 303 505-8760
>>>> On 10/8/18 4:03 PM, Drake wrote:
>>>>> Hello Wrenches,
>>>>>
>>>>> Do you use surge arrestors with multi MPPT input string inverters? 
>>>>> Do you put a separate arrestor on each MPPT input? I find it sort 
>>>>> of pricey using a Midnite Solar arrestor on each string, but have 
>>>>> been doing that. Is there a less expensive approach that is 
>>>>> effective?
>>>>>
>>>>> I believe the Midnite units are the best. Are they worth the expense?
>>>>>
>>>>> Thank you,
>>>>>
>>>>> Drake
>>>>>
>>>>>
>>>>> Drake Chamberlin
>>>>> /Athens Electric LLC
>>>>> OH License 44810
>>>>> CO License 3773
>>>>> NABCEP Certified Solar PV
>>>>> 740-448-7328
>>>>> /http://athens-electric.com/
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>>
>>>>> List Address:
>>>>> RE-wrenches at lists.re-wrenches.org 
>>>>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>>
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>
>>>>> List-Archive:
>>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>>
>>>>> List rules & etiquette:
>>>>> www.re-wrenches.org/etiquette.htm 
>>>>> <http://www.re-wrenches.org/etiquette.htm>
>>>>>
>>>>> Check out or update participant bios:
>>>>> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>>>>
>>>>
>>>>
>>>>
>>>>
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> List Address:
>>>> RE-wrenches at lists.re-wrenches.org 
>>>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> List-Archive:
>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm 
>>>> <http://www.re-wrenches.org/etiquette.htm>
>>>>
>>>> Check out or update participant bios:
>>>> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>>>
>>>
>>> -- 
>>>
>>>          Christopher Warfel, PE
>>>        ENTECH Engineering, Inc.
>>> PO Box 871, Block Island, RI 02807
>>> (401)466-8978
>>>
>>> EEI logo <http://entech-engineering.com>
>>>
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address:
>>> RE-wrenches at lists.re-wrenches.org 
>>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm 
>>> <http://www.re-wrenches.org/etiquette.htm>
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>>
>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: 
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 
>>
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm 
>> <http://www.re-wrenches.org/etiquette.htm>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20181009/3229c0f3/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 2f77d532.jpg
Type: image/jpeg
Size: 17117 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20181009/3229c0f3/attachment.jpg>


More information about the RE-Wrenches mailing list