[RE-wrenches] Conext xw+ 6848 inverter 1.5 minute voltage increase
Dave Angelini Offgrid Solar
offgridsolar at sti.net
Mon Aug 13 11:42:05 EDT 2018
Good point about the neutral ! Go thru the panel/ light circuits and
re-torque. Set up the combox to log L1 and L2. --Dave
On Mon, 13 Aug 2018 09:04:37 -0400, Drake
<drake.chamberlin at redwoodalliance.org> wrote:
> This problem might be due to a neutral connection
> problem in the electrical system. Loose neutral
> connections can put 120 V loads in series. It
> puts loads on both line 1 an line 2 in series for
> 240 V. The high resistance load (the one with the low draw) gets high
> voltage.
>
>
> At 06:23 PM 8/11/2018, you wrote:
>>I am placing this inquiry out to see if anyone
>>else has experienced a similar experience. An
>>electrician friend near Taos, NM, installed a
>>Conext XW+ 6648 inverter on a large 2nd seasonal
>>(remote stand alone PV supplied) vacation home,
>>(used less than 10 weeks per year), it has a
>>large 48 VDC AGM battery (40+kW-Hr) and almost a
>>7.0 kW PV Array and a back-up LP gen-set. It has
>>a Xantrex accessories : Com-Box, charge
>>controllers, bat monitor, etc. The anomaly this
>>system exhibits is that - when the owners are
>>infrequently present - during each evening, for
>>about 90 seconds - the 120vac lights get
>>noticebly brighter. After this brief event, the
>>lights exhibit normal behavior. No lights or
>>appliances are functionally damaged. It is more
>>of a nuisance than an actual problem. This
>>usually happens between 9:30 and midnight. The
>>timing seems to be arbitrary - as no known load
>>either turns on or turns off in conjunction with
>>this event. Xantrex has been consulted and the
>>inverters firm ware has been upgraded and they
>>even sent a replacement inverter control board,
>>which after its replacement nothing changed. As
>>this is quite late at night and has been
>>happening both in winter and in summer months,
>>it is not presently believed to be associated
>>with the PV modules or charge controller.
>>Conventional wisdom implies, that if there is
>>some significant load was cycling in the
>>background - the lights would dim - not
>>brighten. I have never heard of anything like
>>this and was wondering- if any had. There are no
>>known large capacitive loads on the system. Any
>>one seen anything similar, I was asked - as I
>>have been doing systems in New Mexico since 1995
>>and I guessed it was a well/ water pressure
>>bladder tank system related issue . . . but
>>the installer has witnessed this, at night when
>>the water pump and well remained off. ? Item
>>2) some weeks ago, it was noted on this
>>RE-Wrenches thread that some ballast blocks,
>>4†x 8†x 16†were starting to suffer
>>decomposition and a solution was sought, I
>>guessed that this might be due to water seepage
>>and repeated freezing and thawing. Has anyone
>>used an inexpensive masonry sealer painted on
>>the blocks, to stop water wicking to the
>>concrete ballast blocks? There is very thick
>>cinder block paint (UGL) for cinder block
>>foundations that would be quite expensive and
>>polyurethane is very pricey too - I would like
>>to recommend that works successfully and is
>>economical for existing installations rather
>>than replacing hundreds of blocks? Thanks,
>>Daniel O. Duffield NABCEP Certified PV
>>Installation Professional (2005) NM licensed
>>Commercial Electrical Contractor EE98/ER01 IEEE
>>member 23 years
>>_______________________________________________
>>List sponsored by Redwood Alliance List Address:
>>RE-wrenches at lists.re-wrenches.org Change
>>listserver email address & settings:
>>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>List-Archive:
>>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>>List rules & etiquette:
>>www.re-wrenches.org/etiquette.htm Check out or
>>update participant bios: www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
>
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
More information about the RE-Wrenches
mailing list