[RE-wrenches] Conext xw+ 6848 inverter 1.5 minute voltage increase
Drake
drake.chamberlin at redwoodalliance.org
Mon Aug 13 09:04:37 EDT 2018
This problem might be due to a neutral connection
problem in the electrical system. Loose neutral
connections can put 120 V loads in series. It
puts loads on both line 1 an line 2 in series for
240 V. The high resistance load (the one with the low draw) gets high voltage.
At 06:23 PM 8/11/2018, you wrote:
>I am placing this inquiry out to see if anyone
>else has experienced a similar experience. An
>electrician friend near Taos, NM, installed a
>Conext XW+ 6648 inverter on a large 2nd seasonal
>(remote stand alone PV supplied) vacation home,
>(used less than 10 weeks per year), it has a
>large 48 VDC AGM battery (40+kW-Hr) and almost a
>7.0 kW PV Array and a back-up LP gen-set. It has
>a Xantrex accessories : Com-Box, charge
>controllers, bat monitor, etc. The anomaly this
>system exhibits is that - when the owners are
>infrequently present - during each evening, for
>about 90 seconds - the 120vac lights get
>noticebly brighter. After this brief event, the
>lights exhibit normal behavior. No lights or
>appliances are functionally damaged. It is more
>of a nuisance than an actual problem. This
>usually happens between 9:30 and midnight. The
>timing seems to be arbitrary - as no known load
>either turns on or turns off in conjunction with
>this event. Xantrex has been consulted and the
>inverters firm ware has been upgraded and they
>even sent a replacement inverter control board,
>which after its replacement nothing changed. As
>this is quite late at night and has been
>happening both in winter and in summer months,
>it is not presently believed to be associated
>with the PV modules or charge controller.
>Conventional wisdom implies, that if there is
>some significant load was cycling in the
>background - the lights would dim - not
>brighten. I have never heard of anything like
>this and was wondering- if any had. There are no
>known large capacitive loads on the system. Any
>one seen anything similar, I was asked - as I
>have been doing systems in New Mexico since 1995
>and I guessed it was a well/ water pressure
>bladder tank system related issue . . . but
>the installer has witnessed this, at night when
>the water pump and well remained off. ? Item
>2) some weeks ago, it was noted on this
>RE-Wrenches thread that some ballast blocks,
>4â x 8â x 16â were starting to suffer
>decomposition and a solution was sought, I
>guessed that this might be due to water seepage
>and repeated freezing and thawing. Has anyone
>used an inexpensive masonry sealer painted on
>the blocks, to stop water wicking to the
>concrete ballast blocks? There is very thick
>cinder block paint (UGL) for cinder block
>foundations that would be quite expensive and
>polyurethane is very pricey too - I would like
>to recommend that works successfully and is
>economical for existing installations rather
>than replacing hundreds of blocks? Thanks,
>Daniel O. Duffield NABCEP Certified PV
>Installation Professional (2005) NM licensed
>Commercial Electrical Contractor EE98/ER01 IEEE
>member 23 years
>_______________________________________________
>List sponsored by Redwood Alliance List Address:
>RE-wrenches at lists.re-wrenches.org Change
>listserver email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>List-Archive:
>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm Check out or
>update participant bios: www.members.re-wrenches.org
More information about the RE-Wrenches
mailing list