[RE-wrenches] Conext xw+ 6848 inverter 1.5 minute voltage increase
Dave Angelini Offgrid Solar
offgridsolar at sti.net
Sat Aug 11 19:30:14 EDT 2018
Daniel,
No, have not seen this. I would load an SD card into combox and start a
logging program to monitor L1 and L2. Since Schneider replaced the inverter
control board I am at a loss. Your comments seem logical to me also. What
about refrigerator surge? if you still have repair number from Schneider I
would see what they say also. Good Luck!
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridsolar at sti.net
text 209 813 0060
On Sat, 11 Aug 2018 16:23:49 -0600, Daniel Duffield <dduffield at me.com>
wrote:
> I am placing this inquiry out to see if anyone else has experienced a
> similar experience.
>
> An electrician friend near Taos, NM, installed a Conext XW+ 6648
inverter
> on a large 2nd seasonal (remote stand alone PV supplied) vacation home,
> (used less than 10 weeks per year), it has a large 48 VDC AGM battery
> (40+kW-Hr) and almost a 7.0 kW PV Array and a back-up LP gen-set. It has
a
> Xantrex accessories : Com-Box, charge controllers, bat monitor, etc.
> The anomaly this system exhibits is that - when the owners are
> infrequently present - during each evening, for about 90 seconds - the
> 120vac lights get noticebly brighter. After this brief event, the lights
> exhibit normal behavior. No lights or appliances are functionally
damaged.
> It is more of a nuisance than an actual problem. This usually happens
> between 9:30 and midnight. The timing seems to be arbitrary - as no
known
> load either turns on or turns off in conjunction with this event.
> Xantrex has been consulted and the inverters firm ware has been upgraded
> and they even sent a replacement inverter control board, which after its
> replacement nothing changed.
> As this is quite late at night and has been happening both in winter
and
> in summer months, it is not presently believed to be associated with
the
> PV modules or charge controller.
> Conventional wisdom implies, that if there is some significant load was
> cycling in the background - the lights would dim - not brighten. I have
> never heard of anything like this and was wondering- if any had. There
are
> no known large capacitive loads on the system.
> Any one seen anything similar, I was asked - as I have been doing
systems
> in New Mexico since 1995 and I guessed it was a well/ water pressure
> bladder tank system related issue . . . but the installer has
witnessed
> this, at night when the water pump and well remained off. ?
>
> Item 2) some weeks ago, it was noted on this RE-Wrenches thread that
some
> ballast blocks, 4” x 8” x 16” were starting to suffer decomposition and
a
> solution was sought, I guessed that this might be due to water seepage
and
> repeated freezing and thawing.
>
> Has anyone used an inexpensive masonry sealer painted on the blocks, to
> stop water wicking to the concrete ballast blocks? There is very thick
> cinder block paint (UGL) for cinder block foundations that would be
quite
> expensive and polyurethane is very pricey too - I would like to
recommend
> that works successfully and is economical for existing installations
rather
> than replacing hundreds of blocks?
>
> Thanks,
> Daniel O. Duffield
> NABCEP Certified PV Installation Professional (2005)
> NM licensed Commercial Electrical Contractor EE98/ER01
> IEEE member 23 years
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
>
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
--
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridsolar at sti.net
text 209 813 0060
More information about the RE-Wrenches
mailing list