[RE-wrenches] Conext xw+ 6848 inverter 1.5 minute voltage increase
Daniel Duffield
dduffield at me.com
Sat Aug 11 18:23:49 EDT 2018
I am placing this inquiry out to see if anyone else has experienced a similar experience.
An electrician friend near Taos, NM, installed a Conext XW+ 6648 inverter on a large 2nd seasonal (remote stand alone PV supplied) vacation home, (used less than 10 weeks per year), it has a large 48 VDC AGM battery (40+kW-Hr) and almost a 7.0 kW PV Array and a back-up LP gen-set. It has a Xantrex accessories : Com-Box, charge controllers, bat monitor, etc.
The anomaly this system exhibits is that - when the owners are infrequently present - during each evening, for about 90 seconds - the 120vac lights get noticebly brighter. After this brief event, the lights exhibit normal behavior. No lights or appliances are functionally damaged.
It is more of a nuisance than an actual problem. This usually happens between 9:30 and midnight. The timing seems to be arbitrary - as no known load either turns on or turns off in conjunction with this event.
Xantrex has been consulted and the inverters firm ware has been upgraded and they even sent a replacement inverter control board, which after its replacement nothing changed.
As this is quite late at night and has been happening both in winter and in summer months, it is not presently believed to be associated with the PV modules or charge controller.
Conventional wisdom implies, that if there is some significant load was cycling in the background - the lights would dim - not brighten. I have never heard of anything like this and was wondering- if any had. There are no known large capacitive loads on the system.
Any one seen anything similar, I was asked - as I have been doing systems in New Mexico since 1995 and I guessed it was a well/ water pressure bladder tank system related issue . . . but the installer has witnessed this, at night when the water pump and well remained off. ?
Item 2) some weeks ago, it was noted on this RE-Wrenches thread that some ballast blocks, 4” x 8” x 16” were starting to suffer decomposition and a solution was sought, I guessed that this might be due to water seepage and repeated freezing and thawing.
Has anyone used an inexpensive masonry sealer painted on the blocks, to stop water wicking to the concrete ballast blocks? There is very thick cinder block paint (UGL) for cinder block foundations that would be quite expensive and polyurethane is very pricey too - I would like to recommend that works successfully and is economical for existing installations rather than replacing hundreds of blocks?
Thanks,
Daniel O. Duffield
NABCEP Certified PV Installation Professional (2005)
NM licensed Commercial Electrical Contractor EE98/ER01
IEEE member 23 years
More information about the RE-Wrenches
mailing list