[RE-wrenches] Conext xw+ 6848 inverter 1.5 minute voltage increase
Ray
ray at solarray.com
Mon Aug 13 14:03:47 EDT 2018
Good Call Drake, I've definitely had that problem before too. Neutral
became disconnected, and the voltage on one leg got so high it damaged
some equipment: garage door opener, heating controls, microwave, oven
controls.... Funny thing was when the loads were roughly balanced,
everything seemed normal; close to 120 vac on each leg, and 240 vac
loads were not effected.
Ray Walters
Remote Solar
303 505-8760
On 8/13/18 7:04 AM, Drake wrote:
> This problem might be due to a neutral connection problem in the
> electrical system. Loose neutral connections can put 120 V loads in
> series. It puts loads on both line 1 an line 2 in series for 240 V.
> The high resistance load (the one with the low draw) gets high voltage.
>
>
> At 06:23 PM 8/11/2018, you wrote:
>> I am placing this inquiry out to see if anyone else has experienced a
>> similar experience. An electrician friend near Taos, NM, installed a
>> Conext XW+ 6648 inverter on a large 2nd seasonal (remote stand alone
>> PV supplied) vacation home, (used less than 10 weeks per year), it
>> has a large 48 VDC AGM battery (40+kW-Hr) and almost a 7.0 kW PV
>> Array and a back-up LP gen-set. It has a Xantrex accessories :
>> Com-Box, charge controllers, bat monitor, etc. The anomaly this
>> system exhibits is that - when the owners are infrequently present -
>> during each evening, for about 90 seconds - the 120vac lights get
>> noticebly brighter. After this brief event, the lights exhibit normal
>> behavior. No lights or appliances are functionally damaged. It is
>> more of a nuisance than an actual problem. This usually happens
>> between 9:30 and midnight. The timing seems to be arbitrary - as no
>> known load either turns on or turns off in conjunction with this
>> event. Xantrex has been consulted and the inverters firm ware has
>> been upgraded and they even sent a replacement inverter control
>> board, which after its replacement nothing changed. As this is quite
>> late at night and has been happening both in winter and in summer
>> months, it is not presently believed to be associated with the PV
>> modules or charge controller. Conventional wisdom implies, that if
>> there is some significant load was cycling in the background - the
>> lights would dim - not brighten. I have never heard of anything like
>> this and was wondering- if any had. There are no known large
>> capacitive loads on the system. Any one seen anything similar, I was
>> asked - as I have been doing systems in New Mexico since 1995 and I
>> guessed it was a well/ water pressure bladder tank system related
>> issue . . . but the installer has witnessed this, at night when the
>> water pump and well remained off. ? Item 2) some weeks ago, it was
>> noted on this RE-Wrenches thread that some ballast blocks, 4†x
>> 8†x 16†were starting to suffer decomposition and a solution was
>> sought, I guessed that this might be due to water seepage and
>> repeated freezing and thawing. Has anyone used an inexpensive masonry
>> sealer painted on the blocks, to stop water wicking to the concrete
>> ballast blocks? There is very thick cinder block paint (UGL) for
>> cinder block foundations that would be quite expensive and
>> polyurethane is very pricey too - I would like to recommend that
>> works successfully and is economical for existing installations
>> rather than replacing hundreds of blocks? Thanks, Daniel O. Duffield
>> NABCEP Certified PV Installation Professional (2005) NM licensed
>> Commercial Electrical Contractor EE98/ER01 IEEE member 23 years
>> _______________________________________________ List sponsored by
>> Redwood Alliance List Address: RE-wrenches at lists.re-wrenches.org
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out
>> or update participant bios: www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
More information about the RE-Wrenches
mailing list