[RE-wrenches] UL/CSA listed battery monitor?

Dave Angelini Offgrid Solar offgridsolar at sti.net
Tue Jul 10 17:31:20 EDT 2018


I have one question also. Do you have the Nicad data to enter into a
typical shunt based monitor to calibrate it? Without loading the 5 or 6
parameters a quality battery monitor needs, it really is not going to be
that accurate. It is so nice to have the data from a BMS and no shunt
required. Very accurate Soc:)

> This is probably a dumb question, but is the NiCad battery UL listed? 
> Most batteries are not.
>
> Ray Walters
> Remote Solar
> 303 505-8760
>
> On 7/10/18 2:19 PM, bob at midnitesolar.com wrote:
>>
>>
>> I don't know of any listed battery monitors.  Not sure what spec they
>> would be tested to ?
>>
>> However...
>> In Canada, I have heard of systems being individually blessed by
>> inspectors or whoever that
>> include products that don't have listings but everything in the system
>> had to have a listing.
>>
>> I know that this was done for our wind Clipper in Canada not long ago.
>>
>> Email me directly and I can try to find the particulars of that
>> situation if it might help here.
>>
>> Thanks,
>> boB
>>
>>
>> On 7/10/2018 11:36 AM, bob at midnitesolar.com wrote:
>>>
>>>
>>> Just to clarify, MidNite has two (2) battery monitors....  Sort of...
>>>
>>> The  MNBCM that Tom referred to is a shunt-less voltage monitor that
>>> lets you know when
>>> the battery has not received an Absorb charge cycle for 1 week and 2
>>> weeks.  It also has
>>> somewhat of a voltage meter.  It is purely based on battery voltage
>>> and looks for the rise
>>> in voltage for an accumulated of around 2 hours or so...  It has a
>>> semi-circle of LEDs on it.
>>>
>>> Then the Whizbang Junior is a 500A @ 50 mV shunt tack-on circuit
>>> board that connects to
>>> the MidNite Classic or Kid charge controllers that calculates State
>>> Of Charge based on
>>> Amp-Hours in and out of the bank.
>>>
>>> Thanks,
>>> boB
>>>
>>>
>>> On 7/10/2018 9:09 AM, Dan Fink wrote:
>>>> The Midnite battery monitor requires a shunt, it piggybacks onto
>>>> that shunt.
>>>>
>>>> Dan Fink
>>>> Professor of Solar Energy Technology, Ecotech Institute
>>>> IREC Certified Instructor™ for:
>>>> ~ PV Installation Professional
>>>> ~ Small Wind Installer
>>>> Executive Director, Buckville Energy
>>>> NABCEP Registered Continuing Education Providers™
>>>> NABCEP Associate
>>>>
>>>> 970.672.4342
>>>>
>>>>
>>>> On Tue, Jul 10, 2018 at 8:53 AM, Tom Duffy <Tom at solar-biz.com
>>>> <mailto:Tom at solar-biz.com>> wrote:
>>>>
>>>>     Look at either the BlueSky IPM Pro Remote with shunt or the
>>>>     Schneider Battery monitor. The MidNite Battery monitor is more
>>>>     basic as it has no shunt
>>>>
>>>>     Kind regards
>>>>
>>>>     *Tom Duffy*
>>>>
>>>>     *Senior Solar Design Engineer*
>>>>
>>>>     Solar-Biz-new-logo-800X300
>>>>
>>>>     Your 5-star rating really matters to us. Click to rate!
>>>>     <https://goo.gl/WVpOYr> Solar Biz™ team workshard to provide you
>>>>     the best customer service. If we don't deserve a 5-star rating,
>>>>     please contact us directly. We'll do what it takes to win your
>>>>     approval.
>>>>
>>>>     */Please note my new E-Mail/*
>>>>
>>>>     *E-Mail: **tom at solar-biz.com <mailto:tom at solar-biz.com>*
>>>>
>>>>     *Main Number: **888-826-0939*
>>>>
>>>>     *Panama Office: **507-836-5588 X 122*
>>>>
>>>>     *Direct Toll Free:**888-503-6772*
>>>>
>>>>     *International: **575-539-2111 X 122*
>>>>
>>>>     *SKYPE Address: **thesolarbiz (/e-mail first/)*
>>>>
>>>>     /I love nuclear energy! It's just that I prefer fusion to
>>>>     fission. And it just so happens that there's an enormous fusion
>>>>     reactor safely banked a few million miles from us. It delivers
>>>>     more than we could ever use in just about 8 minutes. And it's
>>>>     wireless!"///
>>>>
>>>>     *Confidentiality Notice*:This message including any attachments
>>>>     is for the sole use of the intended recipient and may contain
>>>>     confidential and privileged information. Any unauthorized
>>>>     review, use, disclosure or distribution is prohibited. If you
>>>>     are not the intended recipient, please contact the sender and
>>>>     delete any copies of this message.
>>>>
>>>>     **
>>>>
>>>>     *From:*RE-wrenches
>>>>     [mailto:re-wrenches-bounces at lists.re-wrenches.org
>>>>     <mailto:re-wrenches-bounces at lists.re-wrenches.org>] *On Behalf
>>>>     Of *Hilton Dier III
>>>>     *Sent:* Monday, July 09, 2018 9:06 PM
>>>>     *To:* re-wrenches at lists.re-wrenches.org
>>>>     <mailto:re-wrenches at lists.re-wrenches.org>
>>>>     *Subject:* [RE-wrenches] UL/CSA listed battery monitor?
>>>>
>>>>     I have a client who needs a monitoring system for a 48V nominal
>>>>     NiCad battery bank on a boat. It's 4 parallel strings of 6V
>>>>     batteries. (Not ideal, I know) It's a passenger boat in Canada
>>>>     so all electrical devices need to be UL/CSA listed. None of the
>>>>     Bogart Engineering monitors are listed.
>>>>
>>>>     Any suggestions appreciated.
>>>>
>>>>     Thanks!
>>>>
>>>>     Hilton
>>>>
>>>>     --
>>>>
>>>>     Hilton Dier III
>>>>
>>>>     Missisquoi River Hydro
>>>>
>>>>     Renewable Energy Design
>>>>
>>>>
>>>>     _______________________________________________
>>>>     List sponsored by Redwood Alliance
>>>>
>>>>     List Address: RE-wrenches at lists.re-wrenches.org
>>>>     <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>
>>>>     Change listserver email address & settings:
>>>>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>     <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>>>
>>>>     List-Archive:
>>>>     http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>     <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>
>>>>
>>>>     List rules & etiquette:
>>>>     www.re-wrenches.org/etiquette.htm
>>>>     <http://www.re-wrenches.org/etiquette.htm>
>>>>
>>>>     Check out or update participant bios:
>>>>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>>>
>>>>
>>>>
>>>>
>>>>
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> List Address:RE-wrenches at lists.re-wrenches.org
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out or update participant bios:
>>>> www.members.re-wrenches.org
>>>>
>>>
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address:RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>


Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail  offgridsolar at sti.net
text 209 813 0060



More information about the RE-Wrenches mailing list