[RE-wrenches] 1/2 HP well pump soft start at 120 VAC
Darryl Thayer
darylsolar1 at gmail.com
Fri Feb 9 22:25:03 EST 2018
Dana my 1/2 HP 240 volt pump draws about < 2 amps, which is maybe 3.3 amps
if it is 120 volts. I wonder if the high volt drop is leaving your pump in
locked rotor for a long time, in which case a soft start will not help.
Perhaps a buck-boost transformer (about 150 watts) boosting 16% would get
the pump started faster? Do the wire size and length for calculating volt
drop. then use a 3.3 amp soft start.
On Fri, Feb 9, 2018 at 6:24 PM, <penobscotsolar at midmaine.com> wrote:
> Hi Dana,
> We have been using Grundfos SQ-O 1/2 hp, 5 GPM (or they have a 10 GPM
> model) soft start pumps for years, with great outcomes. We have sold 60
> or so over the years with no returns.
>
> Daryl
>
>
>
> > Hey all you solar wise guys,
>
>
>
>
> >
> >
> >
> > I am looking for a recommendation based on your experience, not just data
> > sheets for a 120 volt-9.8 amp-1/2HP well pump soft starter. Every time
> the
> > well pump starts the SW4024 groans and the lights flicker.
> >
> >
> >
> > There are a lot of units that claim to soft start a ½ HP, but the reality
> > is
> > that they claim ½ HP but are limited to 3.3 amp+/- output. I asked how
> > this
> > is and was met with the usual, “gee gosh I am not sure.” I have one in
> > hand
> > now from ABB that is guilty of this claim.
> >
> >
> >
> > Some units claim to meet the spec but then you must limit the wire length
> > to
> > 30 meters. The well is 150’ from the house & 120 ft deep so a 270’ wire
> > run
> > with what the well guy threw in 18 years ago. VFW cable [multi strand
> > cable]
> > is a partial answer but not down in the well.
> >
> > Somewhere down the road the inverter & the well pump will get replaced
> but
> > for now it is working. The newer 3PH wild AC drives are amazing on a
> > Radian
> > Inverter. You cannot even tell the well is pumping till it has been for a
> > while and the fans kick on.
> >
> >
> >
> > Suggestions & directions that have proven reliable for you?
> >
> > Thanks.
> >
> >
> >
> >
> >
> > ------------------------------------------------------------
> ----------------
> >
> > Dana Orzel Great Solar Works, Inc.
> >
> > C - 208.721.7003 dana at solarwork.com
> >
> > Idaho Contractor - # 028765 Idaho PV # 028374
> >
> > NABCEP # 051112-136 www.solarwork.biz
> > <http://www.solarwork.biz>
> >
> > "Responsible Technologies for Responsible People since 1988"
> >
> > P Please consider the environment before printing this email.
> >
> >
> >
> >
> >
> > _______________________________________________
> > List sponsored by Redwood Alliance
> >
> > List Address: RE-wrenches at lists.re-wrenches.org
> >
> > Change listserver email address & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > List-Archive:
> > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
> >
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> >
> > Check out or update participant bios:
> > www.members.re-wrenches.org
> >
> >
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180209/843b56a8/attachment.htm>
More information about the RE-Wrenches
mailing list