WrenchesI think its in the inverter or battery but somewhere before it leaves the inverter flickering lights indicates the inverter is seeing the issue up close, a 4 k inverter is 33 amps AC but Over 166 from the 24 volt batteries if the load if half that with lights and inverter is strugling need to look at the battery voltage including cable drop. I have seen this quite a few times over the years.Jerry


Sent from my Verizon, Samsung Galaxy smartphone

-------- Original message --------
From: Darryl Thayer <darylsolar1 at gmail.com> 
Date: 2/9/18  5:25 PM  (GMT-10:00) 
To: RE-wrenches <re-wrenches at lists.re-wrenches.org> 
Subject: Re: [RE-wrenches] 1/2 HP well pump soft start at 120 VAC 

Dana my 1/2 HP 240 volt pump draws about < 2 amps, which is maybe 3.3 amps if it is 120 volts.  I wonder if the high volt drop is leaving your pump in locked rotor for a long time, in which case a soft start will not help.  Perhaps a buck-boost transformer  (about 150 watts) boosting 16% would get the pump started faster?  Do the wire size and length for calculating volt drop.  then use a 3.3 amp soft start.       
On Fri, Feb 9, 2018 at 6:24 PM,  <penobscotsolar at midmaine.com> wrote:
Hi Dana,

   We have been using Grundfos SQ-O 1/2 hp, 5 GPM (or they have a 10 GPM

model) soft start pumps for years, with great outcomes. We have sold 60

or so over the years with no returns.



Daryl







> Hey all you solar wise guys,









>

>

>

> I am looking for a recommendation based on your experience, not just data

> sheets for a 120 volt-9.8 amp-1/2HP well pump soft starter. Every time the

> well pump starts the SW4024 groans and the lights flicker.

>

>

>

> There are a lot of units that claim to soft start a ½ HP, but the reality

> is

> that they claim ½ HP but are limited to 3.3 amp+/- output. I asked how

> this

> is and was met with the usual, “gee gosh I am not sure.” I have one in

> hand

> now from ABB that is guilty of this claim.

>

>

>

> Some units claim to meet the spec but then you must limit the wire length

> to

> 30 meters. The well is 150’ from the house & 120 ft deep so a 270’ wire

> run

> with what the well guy threw in 18 years ago. VFW cable [multi strand

> cable]

> is a partial answer but not down in the well.

>

> Somewhere down the road the inverter & the well pump will get replaced but

> for now it is working. The newer 3PH wild AC drives are amazing on a

> Radian

> Inverter. You cannot even tell the well is pumping till it has been for a

> while and the fans kick on.

>

>

>

> Suggestions & directions that have proven reliable for you?

>

> Thanks.

>

>

>

>

>

> ----------------------------------------------------------------------------

>

> Dana Orzel                              Great Solar Works, Inc.

>

> C - 208.721.7003                       dana at solarwork.com

>

> Idaho Contractor - # 028765         Idaho PV # 028374

>

> NABCEP # 051112-136                       www.solarwork.biz

> <http://www.solarwork.biz>

>

> "Responsible Technologies for Responsible People since 1988"

>

> P Please consider the environment before printing this email.

>

>

>

>

>

> _______________________________________________

> List sponsored by Redwood Alliance

>

> List Address: RE-wrenches at lists.re-wrenches.org

>

> Change listserver email address & settings:

> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

>

> List-Archive:

> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

>

> List rules & etiquette:

> www.re-wrenches.org/etiquette.htm

>

> Check out or update participant bios:

> www.members.re-wrenches.org

>

>





_______________________________________________

List sponsored by Redwood Alliance



List Address: RE-wrenches at lists.re-wrenches.org



Change listserver email address & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org



List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html



List rules & etiquette:

www.re-wrenches.org/etiquette.htm



Check out or update participant bios:

www.members.re-wrenches.org





-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180209/9921ef49/attachment.htm>


More information about the RE-Wrenches mailing list