[RE-wrenches] 1/2 HP well pump soft start at 120 VAC
penobscotsolar at midmaine.com
penobscotsolar at midmaine.com
Fri Feb 9 19:24:43 EST 2018
Hi Dana,
We have been using Grundfos SQ-O 1/2 hp, 5 GPM (or they have a 10 GPM
model) soft start pumps for years, with great outcomes. We have sold 60
or so over the years with no returns.
Daryl
> Hey all you solar wise guys,
>
>
>
> I am looking for a recommendation based on your experience, not just data
> sheets for a 120 volt-9.8 amp-1/2HP well pump soft starter. Every time the
> well pump starts the SW4024 groans and the lights flicker.
>
>
>
> There are a lot of units that claim to soft start a ½ HP, but the reality
> is
> that they claim ½ HP but are limited to 3.3 amp+/- output. I asked how
> this
> is and was met with the usual, âgee gosh I am not sure.â I have one in
> hand
> now from ABB that is guilty of this claim.
>
>
>
> Some units claim to meet the spec but then you must limit the wire length
> to
> 30 meters. The well is 150â from the house & 120 ft deep so a 270â wire
> run
> with what the well guy threw in 18 years ago. VFW cable [multi strand
> cable]
> is a partial answer but not down in the well.
>
> Somewhere down the road the inverter & the well pump will get replaced but
> for now it is working. The newer 3PH wild AC drives are amazing on a
> Radian
> Inverter. You cannot even tell the well is pumping till it has been for a
> while and the fans kick on.
>
>
>
> Suggestions & directions that have proven reliable for you?
>
> Thanks.
>
>
>
>
>
> ----------------------------------------------------------------------------
>
> Dana Orzel Great Solar Works, Inc.
>
> C - 208.721.7003 dana at solarwork.com
>
> Idaho Contractor - # 028765 Idaho PV # 028374
>
> NABCEP # 051112-136 www.solarwork.biz
> <http://www.solarwork.biz>
>
> "Responsible Technologies for Responsible People since 1988"
>
> P Please consider the environment before printing this email.
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
More information about the RE-Wrenches
mailing list