[RE-wrenches] PV to 208v 3-phase with high leg
Darryl Thayer
daryl_solar at yahoo.com
Fri Apr 8 00:30:26 EDT 2011
the usual 208 3 phase is Y and not have high leg. sometimes you will measure up
to 208 on the high leg of at Delta high leg to neutral. If it is Delta 3 phase
120-240 and a 200 about volt high leg, connect across the 240 volt legs, I e
that is across each phase they should be 240 each leg to leg connect the neutral
only if you have one in that phase. both Fronius and SMA have nice drawings in
their installation guidelines or at their training courses.
________________________________
From: Aladdin Solar <cpickard at aladdinsolar.com>
To: re-wrenches at lists.re-wrenches.org
Sent: Thu, April 7, 2011 11:06:55 PM
Subject: [RE-wrenches] PV to 208v 3-phase with high leg
What is the best approach to interconnecting with a 208 volt 3-phase
service having a high leg? Small to medium sized PV systems.
Charlie Pickard
Aladdin Solar