Charlie,
The installation manuals for the inverters you work with should clarify the
acceptable service configurations. That¹s where I would start. (Actually,
verify the service type first by having your electrician take line-to-line
and line-to-neutral measurements at the service.) If you¹re talking about a
240 delta service with a 208 V high leg, you could interconnect a 3-phase
central inverter that doesn¹t require a neutral connection; I believe Satcon
fits this description. Or you could stack single-phase inverters
line-to-line with at least one of the inverters configured such that it
doesn¹t need to see the neutral. There may be a specific pin configuration
that you need to set inside the inverter to enable operation without the
neutral.
This John Berdner article on scaling up PV system designs appeared in the
very first issue of SolarPro and includes some electrical service type
diagrams that may be helpful:
http://solarprofessional.com/article/?file=SP1_1_pg32_Berdner
David Brearley, Senior Technical Editor
SolarPro magazine
NABCEP Certified PV Installer
david.brearley at solarprofessional.com
Direct: 541.261.6545
On 4/7/11 11:06 PM, "Aladdin Solar" <cpickard at aladdinsolar.com> wrote:
> What is the best approach to interconnecting with a 208 volt 3-phase service
> having a high leg? Small to medium sized PV systems.
>
> Charlie Pickard
> Aladdin Solar
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20110408/57518564/attachment-0001.htm>
More information about the RE-Wrenches
mailing list