<html><head><style type="text/css"><!-- DIV {margin:0px;} --></style></head><body><div style="font-family:times new roman,new york,times,serif;font-size:12pt"><div>the usual 208 3 phase is Y and not have high leg.&nbsp; sometimes you will measure up to 208 on the high leg of at Delta high leg to neutral.&nbsp; If it is Delta 3 phase 120-240 and a 200 about volt high leg, connect across the 240 volt legs, I e that is across each phase they should be 240 each leg to leg connect the neutral only if you have one in that phase.&nbsp; both Fronius and SMA have nice drawings in their installation guidelines or at their training courses.&nbsp; <br></div><div style="font-family: times new roman,new york,times,serif; font-size: 12pt;"><br><div style="font-family: times new roman,new york,times,serif; font-size: 12pt;"><font face="Tahoma" size="2"><hr size="1"><b><span style="font-weight: bold;">From:</span></b> Aladdin Solar
 &lt;cpickard@aladdinsolar.com&gt;<br><b><span style="font-weight: bold;">To:</span></b> re-wrenches@lists.re-wrenches.org<br><b><span style="font-weight: bold;">Sent:</span></b> Thu, April 7, 2011 11:06:55 PM<br><b><span style="font-weight: bold;">Subject:</span></b> [RE-wrenches] PV to 208v 3-phase with high leg<br></font><br>


 
 
<style></style>

<div><font face="Arial" size="2">What is the best approach to interconnecting with a 
208 volt 3-phase service&nbsp;having a high leg?&nbsp;Small to medium 
sized&nbsp;PV systems.</font></div>
<div><font face="Arial" size="2"></font>&nbsp;</div>
<div><font face="Arial" size="2">Charlie Pickard<br>Aladdin 
Solar<br></font></div></div></div>
</div></body></html>