I don't think you need 100A 200+ VDC rated breakers.  You should need 25
amp 200 volt, and 100 amp ~70+ VDC rated breakers, assuming a 48v
battery bank.  15 amp 200 VDC breakers on the array side if you have a
24v battery (which could also then serve the handy function of series
overcurrent protection).

The one big advantage of the high voltage controllers is the array side
is kept at low current.

Also keep in mind that (690.7(D), Circuits Over 150V to Ground, adds a
limitation that live parts "shall not be accessible to other than
qualified personnel," and the FPN then refers us to 110.27 and 210.6.
Dead front covers on equipment, at the least.

On a separate discussion, I'm still trying to figure out WTF the FPN
refers us to 210.6, as it seems to apply to branch circuits &
luminaires.  Unless we're supposed to consider the charge controller a
"permanently connected utilization equipment...?"

 
------------------------------------------------------------

Phil Undercuffler
Director, Battery-based and Off-grid
Conergy, Inc.
Our World is Full of Energy
 
1730 Camino Carlos Rey Suite 103
Santa Fe NM 87507 USA
Office | 505.216.3841
Fax | 505.473.3830
www.conergy.us

------------------------------------------------------------ 
-----Original Message-----
From: Kirpal Khalsa [mailto:solarworks at gmail.com] 
Sent: Wednesday, June 25, 2008 7:19 AM
To: RE-wrenches at topica.com
Subject: 200VDC breakers.... formerly Plug-in Hybrid kWh/day
[RE-wrenches]

On   your first point.......200+VDC chargers.......Any one know where
to get some 200+VDC 100A breakers.....Apollo Solar is releasing their
T100 and it has a 200VDC max input......Would be handy especially for
strings of 4 Evergreen panels in series in off battery based
applications....


-- 
Sunny Regards,
Kirpal Khalsa
NABCEP Certified Solar PV Installer TM
Renewable Energy Systems


On Tue, Jun 24, 2008 at 8:57 PM, Ray Walters <walters at taosnet.com>
wrote:
>
> 200+ vdc solar charge controllers,
> Vehicle Integrated P V, blown electric motors,
> 4000 amp surges, Li+ battery charging,
> arrays actually improving top speed....
>
> EVs are the fun side of the business.
> And part of our future.
>
> Ray
>
>> rish at calsolareng.com writes:
>>
>> I think  this tie-in between EV and PV is a winner. Any comments
would  be
>> appreciated.
>>
>>
>>
>
>> Only that this is my next goal. Being offgrid and do onsite charging
with
>> the ability to do a 50mi round trip.  The big question for me is how
long
>>  do I
>> need to wait for the right vehicle.
>>
>> Don Loweburg
>>
>>
>>
>
>
> - - - -
> Hosted by Home Power magazine
>
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages:
http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Moderator: michael.welch at homepower.com
>
>


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------



More information about the RE-Wrenches mailing list