Robin Gudgel at Midnite is having some CBI breakers developed and tested for
use with his Classic charge controller, which will allow as high as 250 vdc
input. I'm sure he'll announce on Midnite's website when they're available.
I don't know whether 100A will be available, though.
You may also use a fused DC-rated disconnect; likely way cheaper than a GJ
and enclosure.
Allan at Positive Energy
-----Original Message-----
From: Kurt Albershardt [mailto:info at es-ee.com]
Sent: Wednesday, June 25, 2008 9:19 AM
--On Wednesday, June 25, 2008 5:19 AM -0800 Kirpal Khalsa
<solarworks at gmail.com> wrote:
> Any one know where to get some 200+VDC 100A breakers
The 2-pole Heinemann GJ series are rated for 250 VDC, with other variants
handling up to 750 VDC.
A number of the Square-D breakers carry DC ratings (up to 550 VDC for UPS
applications.)
- - - -