200VDC breakers.... formerly Plug-in Hybrid kWh/day [RE-wrenches]

Ray Walters walters at taosnet.com
Wed Jun 25 12:50:11 EDT 2008


<x-flowed>


This started with the EV idea, we're solar charging vehicle batteries  
with nominal voltages of 120 to 156 vdc. So we're not even stepping  
down the array voltage.
We've only had one supplier (Solar Converters Inc in Canada) that  
could make us a controller to do this.
We only need currents below 10 amps, since you can only put so many  
modules on a vehicle.
We've been using Heinemans and Midnite breakers at these voltages for  
years, but we're not constrained by UL or the NEC when working on EVs.
We just follow standard practices of the EV world.

Ray

On Jun 25, 2008, at 9:58 AM, Phil Undercuffler wrote:

>
> I don't think you need 100A 200+ VDC rated breakers.  You should  
> need 25
> amp 200 volt, and 100 amp ~70+ VDC rated breakers, assuming a 48v
> battery bank.  15 amp 200 VDC breakers on the array side if you have a
> 24v battery (which could also then serve the handy function of series
> overcurrent protection).
>
> The one big advantage of the high voltage controllers is the array  
> side
> is kept at low current.
>
> Also keep in mind that (690.7(D), Circuits Over 150V to Ground, adds a
> limitation that live parts "shall not be accessible to other than
> qualified personnel," and the FPN then refers us to 110.27 and 210.6.
> Dead front covers on equipment, at the least.
>
> On a separate discussion, I'm still trying to figure out WTF the FPN
> refers us to 210.6, as it seems to apply to branch circuits &
> luminaires.  Unless we're supposed to consider the charge controller a
> "permanently connected utilization equipment...?"
>
>
> ------------------------------------------------------------
>
> Phil Undercuffler
> Director, Battery-based and Off-grid
> Conergy, Inc.
> Our World is Full of Energy
>
> 1730 Camino Carlos Rey Suite 103
> Santa Fe NM 87507 USA
> Office | 505.216.3841
> Fax | 505.473.3830
> www.conergy.us
>
> ------------------------------------------------------------
> -----Original Message-----
> From: Kirpal Khalsa [mailto:solarworks at gmail.com]
> Sent: Wednesday, June 25, 2008 7:19 AM
> To: RE-wrenches at topica.com
> Subject: 200VDC breakers.... formerly Plug-in Hybrid kWh/day
> [RE-wrenches]
>
> On   your first point.......200+VDC chargers.......Any one know where
> to get some 200+VDC 100A breakers.....Apollo Solar is releasing their
> T100 and it has a 200VDC max input......Would be handy especially for
> strings of 4 Evergreen panels in series in off battery based
> applications....
>
>
> -- 
> Sunny Regards,
> Kirpal Khalsa
> NABCEP Certified Solar PV Installer TM
> Renewable Energy Systems
>
>
> On Tue, Jun 24, 2008 at 8:57 PM, Ray Walters <walters at taosnet.com>
> wrote:
>>
>> 200+ vdc solar charge controllers,
>> Vehicle Integrated P V, blown electric motors,
>> 4000 amp surges, Li+ battery charging,
>> arrays actually improving top speed....
>>
>> EVs are the fun side of the business.
>> And part of our future.
>>
>> Ray
>>
>>> rish at calsolareng.com writes:
>>>
>>> I think  this tie-in between EV and PV is a winner. Any comments
> would  be
>>> appreciated.
>>>
>>>
>>>
>>
>>> Only that this is my next goal. Being offgrid and do onsite charging
> with
>>> the ability to do a 50mi round trip.  The big question for me is how
> long
>>>  do I
>>> need to wait for the right vehicle.
>>>
>>> Don Loweburg
>>>
>>>
>>>
>>
>>
>> - - - -
>> Hosted by Home Power magazine
>>
>> To send a message: RE-wrenches at topica.com
>>
>> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
>>
>> List rules & how to change your email address:
>> www.mrsharkey.com/wrenches/etiquette.php
>>
>> Check out participant bios: www.mrsharkey.com/wrenches/
>>
>> Moderator: michael.welch at homepower.com
>>
>>
>
>
> - - - -
> Hosted by Home Power magazine
>
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://lists.topica.com/lists/RE- 
> wrenches/read
>
> List rules & how to change your email address: www.mrsharkey.com/ 
> wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Moderator: michael.welch at homepower.com
>

R. Walters
Solarray.com
NABCEP # 04170442	




--
[Non-text portions of this message have been removed]


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------


</x-flowed>


More information about the RE-Wrenches mailing list