equipment grounding conductors [RE-wrenches]

Drake Chamberlin Drake.Chamberlin at redwoodalliance.org
Wed Oct 24 15:53:15 EDT 2007


Hi Larry,

This is the issue of the size of the equipment grounding conductor, and 
if we can use EMT conduit for an equipment ground as permitted by 
250.118.  The equipment grounding conductor size for PV is covered in 
690.45.  

Thanks,

Drake 


Larry Crutcher, Starlight Solar wrote:
> 
> 
> Drake Chamberlin wrote:
> > 
> > Correction:
> > 
> > We size the wire for 125% short circuit current.
> > 
> > Drake 
> > 
> 
> Drake,
> 
> The 125% rule is correct for determining the ampacity of your source 
> circuit current. However, you must add an additional 125% to size the 
> conductors and the overcurrent protection. This means you need 156% of 
> the Isc for all PV wire runs and the fuses or breakers protecting each 
> string. Also, do not forget to derate for temperature.
> 
> Larry Crutcher
> Starlight Solar
> Yuma, AZ
> Renewable Energy Products Powered by STARLIGHT


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------



More information about the RE-Wrenches mailing list