Drake Chamberlin wrote:
> 
> Correction:
> 
> We size the wire for 125% short circuit current.
> 
> Drake 
> 

Drake,

The 125% rule is correct for determining the ampacity of your source 
circuit current. However, you must add an additional 125% to size the 
conductors and the overcurrent protection. This means you need 156% of 
the Isc for all PV wire runs and the fuses or breakers protecting each 
string. Also, do not forget to derate for temperature.