equipment grounding conductors [RE-wrenches]
Larry Crutcher, Starlight Solar
larry at starlightsolar.com
Wed Oct 24 16:06:28 EDT 2007
Drake Chamberlin wrote:
>
> Hi Larry,
>
> This is the issue of the size of the equipment grounding conductor, and
> if we can use EMT conduit for an equipment ground as permitted by
> 250.118. The equipment grounding conductor size for PV is covered in
> 690.45.
>
> Thanks,
>
> Drake
>
>
> Larry Crutcher, Starlight Solar wrote:
> >
> >
> > Drake Chamberlin wrote:
> > >
> > > Correction:
> > >
> > > We size the wire for 125% short circuit current.
> > >
> > > Drake
> > >
> >
> > Drake,
> >
> > The 125% rule is correct for determining the ampacity of your source
> > circuit current. However, you must add an additional 125% to size the
> > conductors and the overcurrent protection. This means you need 156% of
> > the Isc for all PV wire runs and the fuses or breakers protecting each
> > string. Also, do not forget to derate for temperature.
> >
> > Larry Crutcher
> > Starlight Solar
> > Yuma, AZ
> > Renewable Energy Products Powered by STARLIGHT
Ohhh...I have always used the 1.56 rule for my ground conductor as well
as the current carrying conductors. Guess I can save a buck on my next
install! More like $50 with copper prices where they are.
Thank you for the education.
Larry
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list