Piss poor Trace SW preformance in "sell" mode. [RE-wrenches]
Carl Emerson
freepower at freepower.co.nz
Tue Oct 17 21:20:02 EDT 2000
Further to my comment earlier. I guess that the wind option would require another
auxiliary relay to come in just under the sell voltage set point and reconnect the
grid at night during windy conditions.
Maybe both the solar and wind could be simply controlled this way ??
i.e. lower the float voltage, use one of the auxiliary relays (as a slave driving a
larger AC contactor to disconnect the grid just under the sell voltage. This would
mean at night the voltage would float down, the grid would disconnect, the unit
would go into search mode, (unless the wind was blowing.) In the morning when the
solar comes in the voltage rises and the relay reconnects the grid.
If the owner had heavy loads at night a second auxiliary relay would reconnect the
grid just above the lowered float voltage providing grid power to keep the
batteries charged.
To simple to be possible ??
--
Regards,
Carl Emerson
Manager
FREEPOWER LTD. "Harnessing Natural Energy"
AUCKLAND
356 East Coast Road, Mairangi Bay, P.O. Box 68-247, AUCKLAND, New
Zealand.
Voice +64 9 478-0404 Mobile 021-633999 Cellfax 021-2919399
Fax +64 9 478-0405 Email emerson at freepower.co.nz
- - - - - - -
To send a message:
RE-wrenches at topica.com
The archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
To unsubscribe send a message to:
RE-wrenches-unsubscribe at topica.com
To check out the other RE-Wrench participants:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine:
www.homepower.com
For info contact list moderator by email:
michael.welch at homepower.com
___________________________________________________________
T O P I C A The Email You Want. http://www.topica.com/t/16
Newsletters, Tips and Discussions on Your Favorite Topics
More information about the RE-Wrenches
mailing list