Carl Emerson wrote on the SW efficiency topic:
> 
> 
> Firstly I wondered, following on from Travis, to lower the float voltage and
> drop out the grid at night with a photo-relay to allow the unit to enter search
> mode . This would seem to address both sources of excess drain.

Greetings Carl,

You are on the right track here, as the Trace drops into inverter mode
when AC1 is disconnected.  It would be my understanding that in order to
maintain high efficiency though, the inverter can't be reconnected to
the utility until after battery voltage comes up above the bulk voltage
setting (solar), or the inverter will go into a charge cycle.  My
thinking may be wrong here but I think the inverter will initialize a
bulk/absorption/and then float charge cycle every time power is "lost"
to AC1 and the unit transfers over to just being an inverter.  By
waiting to reconnect to the grid until voltage is above bulk setting, no
additional energy should come from the utility to bring this about.  I
think this is the logic behind using a voltage controlled "AUX" relay to
pull in that contactor the next day.

Another question I still have is will the inverter do a low battery
transfer (LBX) type thing and utilize the grid to charge the battery if
the battery voltage goes too low while the inverter is in the inverter
mode (disconnected from the grid).   While in LBX, the inverter would go
to AC1 for juice.  In sell mode, (and switched over to inverter from
loss of AC1) would we utilize AC2 input with utility also available
there?  

Kurt Nelson

> - - - - - - -
> To send a message:
>  RE-wrenches at topica.com
> 
> The archive of previous messages:
>  http://www.topica.com/lists/RE-wrenches/
> 
> To unsubscribe send a message to:
>  RE-wrenches-unsubscribe at topica.com
> 
> To check out the other RE-Wrench participants:
>  www.mrsharkey.com/wrenches/index.html
> 
> Hosted by Home Power magazine:
>  www.homepower.com
> 
> For info contact list moderator by email:
>  michael.welch at homepower.com
> ___________________________________________________________
> T O P I C A  The Email You Want. http://www.topica.com/t/16
> Newsletters, Tips and Discussions on Your Favorite Topics

- - - - - - -
To send a message:
 RE-wrenches at topica.com

The archive of previous messages: 
 http://www.topica.com/lists/RE-wrenches/

To unsubscribe send a message to: 
 RE-wrenches-unsubscribe at topica.com

To check out the other RE-Wrench participants:
 www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine: 
 www.homepower.com

For info contact list moderator by email:
 michael.welch at homepower.com
___________________________________________________________
T O P I C A  The Email You Want. http://www.topica.com/t/16
Newsletters, Tips and Discussions on Your Favorite Topics


More information about the RE-Wrenches mailing list