Lockable Disconnect. [RE-wrenches]
Michael Welch, Home Power
michael.welch at homepower.com
Wed Jun 7 15:00:35 EDT 2000
Kurt Nelson, SunWise wrote at 10:38 AM 6/7/2000 -0700:
>John, I have also used the Square D air conditioning disconnect and in my
>case the 60 amp version. It is small and cheap ($30US?). It looks like it
>contains a 60 amp 2 pole breaker, but is only a switch, and is lockable. I
>have also had good luck discussing options and alternatives with the
>utility. Alliant power even waved the disconnect in two systems I did when
>I sent them the info on the SW Trace -- Kurt
In CA, PG&E will not allow fuses or breakers in the disconnects because they do not want anything in there that a user would need to get to. PG&E locks the box closed in the on position until and if they ever need to switch it off.
Also, I think these boxes need to have a hole drilled in them to lock in the on position, but there is a handy center-punched spot to do it. A simple matter.
Michael Welch
------------------------
"Society is like a stew. If you don't keep it stirred up, you get a lot of scum on top."
Edward Abbey
Michael Welch, michael.welch at homepower.com www.homepower.com
Associate Editor, Home Power magazine
Office Coordinator, Redwood Alliance
(Not HP mag's #s) 707-822-7884 fax: 707-822-3481
- - - - - - -
To send a message to the list use: <RE-wrenches at topica.com>
To view an archive of previous messages go to: <http://www.topica.com/lists/RE-wrenches/
To unsubscribe send an email message to: <RE-wrenches-unsubscribe at topica.com>
To check out who the other RE-Wrench participants are, go to <http://www.mrsharkey.com/wrenches/>
Hosted by Home Power magazine: <http://www.homepower.com>
for info contact: <michael.welch at homepower.com>
___________________________________________________________
T O P I C A The Email You Want. http://www.topica.com/t/16
Newsletters, Tips and Discussions on Your Favorite Topics
More information about the RE-Wrenches
mailing list