At 11:16 AM 03/23/2000 -0800, you wrote:
>2) the Trace T240 is rated for 3900 watts continously. You're pushing its limits with a 4600 watt generator.
>
>I'd recommend a larger generator (6 kw) min. At least you'd have 20 minimum available amps for household loads if the Trace charger were operating at maximum ouput of 30 amps([6000 watts /120 vac] - 30 = 20 amps). You'll have to use a larger transformer for step down than the T240. Call me if you're interested in finding a source.
AEE has "Autotransformers" in NEMA 1 enclosures, 98% efficient, <0.2% no load idle loss, quiet. 2.5, 4, & 8 kw.
Michael Welch
------------------------
"Society is like a stew. If you don't keep it stirred up, you get a lot of scum on top."
Edward Abbey
Michael Welch, michael.welch at homepower.com www.homepower.com
Associate Editor, Home Power magazine
Office Coordinator, Redwood Alliance
(Not HP mag's #s) 707-822-7884 fax: 707-822-3481
- - - - - - -