I assume the Yamaha is rated for 4600 watts(is that surge or continuious power?). Balancing
is the right idea, but:

1.) the generator is undersized. If the charger is drawing the maximum power from the
generator(30 amps @ 120 vac), thats 3600 watts. There's not may amps left to power household
loads at the same time.

2) the Trace T240 is rated for 3900 watts continously. You're pushing its limits with a 4600
watt generator.

I'd recommend a larger generator (6 kw) min. At least you'd have 20 minimum available amps
for household loads if the Trace charger were operating at maximum ouput of 30 amps([6000
watts /120 vac] - 30 = 20 amps). You'll have to use a larger transformer for step down than
the T240. Call me if you're interested in finding a source.

Kirk, Vt. Solar



cvsolar at aol.com wrote:

> Hi all,
>     I am quoting on a fairly large 48 vdc wind/solar off grid system with 16
> L16P Batteries.  I am planning to use a Yamaha EF4600 generator and am
> wondering if feeding the 240 from the generator into a T240 to balance the
> generator and get more than the 20 amps available in the 120 socket would
> make sense.  I want to minimize generator run time and with the large battery
> bank, it should be able to use close to 25 amps at 120 v to get the 60amp dc
> charger output on the SW4048 and I also need more for the pass through to run
> the house loads.  Has anyone used the balancing transformer?
>
> John Blittersdorf
> Central Vermont Solar and Wind
> - - - - - - -
> To send a message to the list use: <RE-wrenches at topica.com>
>
> To view an archive of previous messages go to: <http://www.topica.com/lists/RE-wrenches/
>
> To unsubscribe send an email message to: <RE-wrenches-unsubscribe at topica.com>
>
> Hosted by Home Power magazine: <http://www.homepower.com>
>
> for info contact: <michael.welch at homepower.com>
> _________________________________________________________
> Enlighten your in-box.         http://www.topica.com/t/15

- - - - - - -
To send a message to the list use: <RE-wrenches at topica.com>

To view an archive of previous messages go to: <http://www.topica.com/lists/RE-wrenches/

To unsubscribe send an email message to: <RE-wrenches-unsubscribe at topica.com>

Hosted by Home Power magazine: <http://www.homepower.com>

for info contact: <michael.welch at homepower.com>
_________________________________________________________
Enlighten your in-box.         http://www.topica.com/t/15


More information about the RE-Wrenches mailing list