[RE-wrenches] PG&E NEM
don energysolarnow.com
don at energysolarnow.com
Fri Apr 10 14:14:08 PDT 2026
Blake G is correct that PGE now requires grid support inverters.
Their portal drop-down menu of approved inverters no longer includes the SB6000US.
They won't let you use what's no longer on their approved list.
You will want to use, or at least claim to use, the SBSE5.8-US-50.
That's what I had to do for the same issue as you.
Or it may be easier to just claim you used the original equipment.
DonB
On Thu, Apr 9, 2026, 7:13?PM William Miller via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Dear Cali-Wrenches:
>
> I finally got my Unirac RM10EVO ballasted ground mount approved. Unirac
> offered a wet stamp service for a modest $350 and that carried the day with
> the building department.
>
> Now I need to submit the paperwork to PG&E. The NEM application was done
> three years ago and the equipment we specified then is of course no longer
> available. PG&E has a rule that you can substitute equipment if the rated
> power is no greater than the application or no less than 80% of the
> application, and we meet that criteria.
>
> The portal will ask if I am using the original equipment. The last one I
> did I fibbed.
>
> Have any of you changed equipment for an existing NEM application? Was it
> a big deal or not? We ended up with a used SB600US. Will the used
> equipment be a problem?
>
>